Fairy Liquid Substance | on ElectriciansForums

Discuss Fairy Liquid Substance in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 24, 2016
Messages
404
Reaction score
92
Location
london
Hello People

Changed a pull chord within the bathroom of a house, the house is currently being rented out and i carried out an accessory change on behalf of the landlord. (pull Chord switch)

During the change i noticed green fairy liquid substance coming from all the accessories in the house including the pull chord which i removed.

I have done some reading online and the substance is toxic and lowers in insulation resistance of the installation.

I have put in writing to the landlord that the situation has the potential to be dangerous and could at some point cause harm to persons or damage property as a way of covering myself.

Is this excessive of me or should i go further and issue a Danger Notice?
 
the green goo is oxidation caused by reactance of the copper to the insulation, probably from the 60's. think as long as you have informed him of the problem, that's enough. a danger notice would be, IMO, a bit over the top. i'd recommend a EICR with IR readings being paramount.
 
Hello People

Changed a pull chord within the bathroom of a house, the house is currently being rented out and i carried out an accessory change on behalf of the landlord. (pull Chord switch)

During the change i noticed green fairy liquid substance coming from all the accessories in the house including the pull chord which i removed.

I have done some reading online and the substance is toxic and lowers in insulation resistance of the installation.

I have put in writing to the landlord that the situation has the potential to be dangerous and could at some point cause harm to persons or damage property as a way of covering myself.

Is this excessive of me or should i go further and issue a Danger Notice?
I'll reply with trepidation Chris, did you do any tests? if no all you can do is, in writing note your initial findings and any recommendations, I realise it's a sort of "not my problem guv" but imo you will have done your duty and reported or highlighted possible problems
 
Tel will need a lay down after being called a "gentleman":grimacing:
been called worse in my time. a customer once referred to me as honest. i had to look that up on wicked pedophile.
 
Thanks Andy I included this in the letter i initially wrote

Which directly contradicts your suggestion that the goo is toxic and affects the simulation of the cable, rather setting yourself up to look like a fool, or possibly worse, aren't you?

As it clearly states in the article the substance is of low flammability, low toxicity and although unsightly does not reduce the electrical integrity of the conductor or cable.
 
Which directly contradicts your suggestion that the goo is toxic and affects the simulation of the cable, rather setting yourself up to look like a fool, or possibly worse, aren't you?

As it clearly states in the article the substance is of low flammability, low toxicity and although unsightly does not reduce the electrical integrity of the conductor or cable.

Read the article again. All of it this time including the solution, then read your post.






Oops!
 
Read the article again. All of it this time including the solution, then read your post.






Oops!

I have read all of it, the third paragraph which is dealing with the existence of this in the normal 'as installed' environment clearly states that it is of low toxicity and has no detrimental impact on the electrical properties. What exactly are you getting at?
The disposal advice is a separate thing and is obviously concerned with waste handling processes. The waste handling process is a different and separate thing from the normal existence and use of the substance.

A substance which is harmless in normal use can fall in to a different category when it becomes a waste product and goes through a waste handling process.
 

Reply to Fairy Liquid Substance in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
315
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
295
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
361

Similar threads

  • Question
The rent deposit schemes are very "Pro" tenant . And tend to always believe a tenant more than a landlord . With smart phones been almost a common...
2
Replies
29
Views
3K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
782

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top