Yo folks,

Not sure that this isn't the second post on same topic, first hasn't appeared. Apologies if so.

Ahead of altering upstairs lighting circuit to add a couple of downlights to an ensuite I carried out the usual tests. Got odd IR results. L-N >1000, L-E >1000, N-E 10!. Did a bit of poking around in the loft and found a spider wired downlight arrangement for main bathroom downlights. JB plus wagos. Removed the arrangement and the IR leapt to >1000. Tested each leg of spider, >1000. As I added eah leg of spider the IR fell away to 10 again. This will be fundamental but it eludes me at present. Any ideas, solutions. Is this typical of spider wired downlights? I tend to daisy chain my own installs.

yours,

Rob
 
So all cable dissed fro CU ?
Yes. When connected to CU, the initial readings were L-N >1000 Mohms, L-E >1000, N-E 7.62. Disconnected the readings were the same for L-N, L-E but had imprived slightly on N-E to 10 Mohms. I realise thats a 'pass' but curiosity got the better of me. The property was rewired 4 years ago with the downlights added shortly afterwards during a bathroom refurb. Theres a cert for the rewire but not for the alteration.
 
Yes. When connected to CU, the initial readings were L-N >1000 Mohms, L-E >1000, N-E 7.62. Disconnected the readings were the same for L-N, L-E but had imprived slightly on N-E to 10 Mohms. I realise thats a 'pass' but curiosity got the better of me. The property was rewired 4 years ago with the downlights added shortly afterwards during a bathroom refurb. Theres a cert for the rewire but not for the alteration.

I can only surmise that when the JB is reconnected ( thats the reason I asked if you tested with the cables not pushed into the JB ) there is, maybe some damp or something, a strange one that isn't it sorry can't be of any help other than my suggestions.
 
I can only surmise that when the JB is reconnected ( thats the reason I asked if you tested with the cables not pushed into the JB ) there is, maybe some damp or something, a strange one that isn't it sorry can't be of any help other than my suggestions.
Cheers Pete, your interest is appreciated. There's some slack in the cables at the jb, I'll remake connections after a visual inspection. I'll let you know if I suss it. Rob.
 

Reply to Falling insulation resistance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
If there are connected loads on the ring circuit, eg sockets with built in USB chargers, then yes, link line and neutral together and test to...
Replies
3
Views
2K
loz2754
L
I use click connectors for all spots so can just unplug them. Then for all light fittings, mount the bases, strip back and Wago. IR it all then...
Replies
2
Views
2K
  • Question
Then you may have been seeing the effect of dielectric absorption. Certain types of insulators including plastics can display an effect where for...
Replies
11
Views
4K
D
Went and had another look last night (as was around his house anyway). Where the Halolite boxes have been attached to a joist and wired in there...
Replies
11
Views
10K
Dave78
D
HI, and sorry to interfere I have a new Fluke 1653B tester and I cant find the KOhms range, but I wonder. 1KOhm is 0.001 MOhm. isnt the tester...
Replies
81
Views
21K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks