Dartmoor
Hi Chaps,
Stumbled across this last week. :eek:
Farmer want the lights changing in his milking parlour for a dairy inspection.
Fabric / rubber insulation on the lighting circuit, insulation and is down to 0.95M. Protected by a rewirable fuse. Installed in pipe with no cpc. All the outbuildings are TT.
My question is do the regs now stipulate that you must run a cpc to each point. or can you rely on the conduit??? (subject to test)
I ran in a 6mm CPC (all i had in the van) to each light from the MET to be on the safe side (zs 35.9 ohms)
I will recommend a PIR and note on the invoice areas of concern
The farmer informs me he is giving up his dairy herd at the end of the year, so he is unlikley to to spend much money.
mmmmmmmmmm
Rgds
G
  • [ElectriciansForums.net] Farm Job
Not certain about this but i think that steel conduit is not recommended for dairy because of corrosion and that they prefer plastic. To my mind the steel is a lot stronger and makes more sense but that 's what i remember.
edit : just had a quick look and yes there are restrictions on conduit use - must be class 2 for internal use and class 4 for external, unfortunately doesn't explain it further just refers you to BS-EN 61386-21.
On reflection stainless steel conduit rings some sort of bell as well in my head, but i believe that costs a fortune!!
Thanks,
Forgot to add initially I did a high current ZS test and the conduit was arcing like mad due to corrosion
at the joints, hence why I added the 6mm's (i know its big but its all i had in the van and clearly asthetics are not the no 1 priority) :eek:
Got to be 50 years old
G
Reckon that if he doesn't get that sorted he could be losing his herd sooner than he intended - what a shocker of an installation:eek:
Too right also look closley at the second pic. There are fuses in the neutrals in addition to the lives. (hence six fuses three circuits)
G
G
now that is out of the history books - i reckon you could be right with your 50 year estimate!
You probs know already but 705.513.2 also says that all equipment in agricultural premises needs to be at least IP44 rated.
Seeing those photo's takes me back.:)
I did a lot of agricultural work as an apprentice and everywhere we went was the same as those pictures.
If it's a dairy then SWA or PVC conduit is the way to go.
Went back today, the farmer has 5 other barns in a simular condition all to be rewired and sorted
May need a hand sorting this lot....;)
Found out it was the first milking parlour in the village 1947....!!!!!!!!!!!!!!!
Thanks all for input
G
hi
any thing that is accessible by livestock needs be double insulated, so galv conduit isnt recomended unles ur running pvc/pvc in it. we normally use pvc conduit or swa. weve just finished a large milking parlour 5 weeks work for 2... nice job!
regards
gary
hi
regards
gary
didn't see that in special locations 705 - i would be interested to know if it is in there or another part of the BRB . The only thing against conduit that i could find was its corrosion resistance.
didn't see that in special locations 705 - i would be interested to know if it is in there or another part of the brb . The only thing against conduit that i could find was its corrosion resistance.
appologies pushrod.... I couldnt see anything in the brb either,i was tought that any thing accessible by livestock had to be double insulated...... Never looked it up though.