Hi I live on a farm with livestock but we are on pme earthing, electric board guys say not many farms on tt around here do I still need to fit 300 ma main switch. Zs is 0.80
-
 
To be honest , unless you are a sparks with the required test gear , do not do it your self .
But depending on your bonding arrangements , ie : earthed metal grids , then you need to be TT and have a max 300ma RCD upfront regardless .
 
705.411.1 , (iii) = 300ma RCD
And as for TT , I have yet to come across a livestock holding that meets the criteria not to be .


Edit ; Don't forget it used to be 500ma before the 17th came out .
 
Last edited:
What's the science behind this?

I can see the logic not having TNCS but why not TNS?

Tns is not a problem, would still require upfront rcd

Due to the rural areas farms are normally in, underground supply cables are not usually practical and usually supplies are from overhead lines

Hence tns is rare
 
I think you need to study the do's and dont's, with regard to livestock farming regulations where PME supplies are concerned. Generally, if livestock quarters with concrete floors are present, then those concrete floors must have a rebar grid that is permanently bonded to the PME's installations MET. If there is no grid present then livestock housing/milking areas must be on a TT earthing system...

Any up-front 300mA RCD needs to be an S type, for discrimination purposes, or you'll find 30mA downstream RCD's taking out that up front unit in fault conditions!!
 

Reply to Farm supply not tt in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top