I have a customer who has seen a massive rise in unit usage, then a bit of nuciance tripping. I went out to investigate & discovered a low IR (about 0.1M) on one of the socket circuits. I disconnected the faulty section to get the power back on & will return another day to bypass the faulty section under the concrete floor to reconnect the rest of the sockets. He didn’t know his previous useage but for a while it has been really high about 20 units every 12 hours. He has called today to say his usage has dropped to under half that. He has no electric water or room heating.

Has anyone else cone across this kinds of usage increase due to a fault?
 
Have you calculated the current which flowed through the fault and thus the power consumed by it?

If it is a 0.1megohms then I make the current 0.0024A and the energy consumption one unit per 2000 hours.

What was tripping? If it was a 30mA RCD then it should be obvious the fault current was generally less than 0.03A

For the fault to use 20 units in 12 hours it would have to be dissipating around 1.6kW as heat, so I'd imagine someone would have noticed the heat or even fire started by this!
 
Have you calculated the current which flowed through the fault and thus the power consumed by it?

If it is a 0.1megohms then I make the current 0.0024A and the energy consumption one unit per 2000 hours.

What was tripping? If it was a 30mA RCD then it should be obvious the fault current was generally less than 0.03A

For the fault to use 20 units in 12 hours it would have to be dissipating around 1.6kW as heat, so I'd imagine someone would have noticed the heat or even fire started by this!
It didn’t seem that plausible, hence me asking on here. Maybe disconnecting some sockets has prevented the MIL plugging in an electric heater?
 
Supplementing some-one else's Heating / Growing more noticeable in winter.
Is reading for a timer currently in off state !
The boiler is an oil combi & there is no immersion heater, I did see 1 freestanding 2kW convector heater but nothing else. Once I reconnect the sockets, I will get him to continue to monitor his usage. I do wonder if his M-I-L is using the convector heater in the conservatory or in the dog kennels, however it is difficult to question a customer once they have said they don't use any heaters!
 
Hi,

Perhaps the faulty area was encountering a non bolted short circuit: considering a single phase, 2wires circuitry for the sockets, under the concrete the L and N are meeting together through a large conducting body (metallic chassis or so) reflecting in heat that the user hasn't noticed for the chassis having a large mass, and being buried under the ground


Dj
 
Hi,

Perhaps the faulty area was encountering a non bolted short circuit: considering a single phase, 2wires circuitry for the sockets, under the concrete the L and N are meeting together through a large conducting body (metallic chassis or so) reflecting in heat that the user hasn't noticed for the chassis having a large mass, and being buried under the ground


Dj

This would create a fault of negligible impedance and cause the circuit protection to operate.

This isn't the issue.
 

Reply to Fault Causing Increased Meter Reading? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top