Last night one of my neighbours asked me to look at a fault which had developed after new skirting boards were fitted!
Today I went round, isolated the circuit and the IR test from the board confimed a L-E very low IR, not too much of a surprise as the RCD wouldn't hold if anything was switched on on the ring.
So I split the ring in the "offending" room and confirmed IR >30 on the leg going back to the board, and IR of >30 on each "link" after that. Odd I thought.
So I refitted the first socket - IR down to about 0.80 Mohms - changed the socket for a new socket, IR value hardly budged - very odd.
Took the socket off the wall and re-tested each leg either side of the socket (and from both ends) , IR>30, scratched my head, put socket back on - IR back down to sub 1 Mohm!!, changed socket again, still below 1Mohm!!
Put if all back together, as I've got previous booked job this afternoon and obviously ring is out of action.
Going back for another look, Friday am probably
Thoughts/suggestions/ideas ???????????
Ta ta for now.
Today I went round, isolated the circuit and the IR test from the board confimed a L-E very low IR, not too much of a surprise as the RCD wouldn't hold if anything was switched on on the ring.
So I split the ring in the "offending" room and confirmed IR >30 on the leg going back to the board, and IR of >30 on each "link" after that. Odd I thought.
So I refitted the first socket - IR down to about 0.80 Mohms - changed the socket for a new socket, IR value hardly budged - very odd.
Took the socket off the wall and re-tested each leg either side of the socket (and from both ends) , IR>30, scratched my head, put socket back on - IR back down to sub 1 Mohm!!, changed socket again, still below 1Mohm!!
Put if all back together, as I've got previous booked job this afternoon and obviously ring is out of action.
Going back for another look, Friday am probably
Thoughts/suggestions/ideas ???????????
Ta ta for now.