Last night one of my neighbours asked me to look at a fault which had developed after new skirting boards were fitted!

Today I went round, isolated the circuit and the IR test from the board confimed a L-E very low IR, not too much of a surprise as the RCD wouldn't hold if anything was switched on on the ring.

So I split the ring in the "offending" room and confirmed IR >30 on the leg going back to the board, and IR of >30 on each "link" after that. Odd I thought.

So I refitted the first socket - IR down to about 0.80 Mohms - changed the socket for a new socket, IR value hardly budged - very odd.

Took the socket off the wall and re-tested each leg either side of the socket (and from both ends) , IR>30, scratched my head, put socket back on - IR back down to sub 1 Mohm!!, changed socket again, still below 1Mohm!!

Put if all back together, as I've got previous booked job this afternoon and obviously ring is out of action.

Going back for another look, Friday am probably

Thoughts/suggestions/ideas ???????????


Ta ta for now.
 
Thinking out of the box here...also try nulling the test leads and then try a few readings there..if youre doing lots of measurements on pendants the leads start coming apart and produce all sorts of funny readings as the dogleg between the lead and the plug starts to wear....you never know!
 
The saga continues..... here are my findings from a brief visit today!

Here is a photo of a reading off my metrel immediately I've done an IR (at 1000v) which shows that there is a "retained" voltage on the cores of the offending "half" of the ring and the IR reading between L & E of 0.96.

Lee.jpg

It takes about 30 seconds for the voltage to drop back to almost zero - suggesting that something is acting as a "capacitor" on said circuit. The other "half" of the ring drops back to zero immediately after the test.

Both the MCB and RCD will hold!

I've tried to trace the circuit round the house and all I can say is that the ring has been extended in a rather unusual fashion!

Any comments, questions, or thoughts would be useful
 
Can you turn it into 2 radials by removing the offending socket? Or as suggested rewire either the cct or just the legs either side of the offending socket. Seems to be cable damage when skirtings replaced, either when old taken off (crushed cables) or when put on (nail or crushed). Crushing seems most likely since when the pressure comes off all will seem normal but squash the cables and you get the short again.
 
Can you turn it into 2 radials by removing the offending socket? Or as suggested rewire either the cct or just the legs either side of the offending socket. Seems to be cable damage when skirtings replaced, either when old taken off (crushed cables) or when put on (nail or crushed). Crushing seems most likely since when the pressure comes off all will seem normal but squash the cables and you get the short again.

If I turn the ring into 2 radials the customer will still have 1 circuit with a fault!

Its the "capacitor" type action I'm puzzled by - if anyone can offer a suggestion or two it would help with fixing the fault!
 
Like Andykoch said Murdoch. Have your 2 radials. The one with the fault will have to lose 1 socket. Wants to keep that socket, could you disconnect it (removing the fault), then spur from another socket to re supply power to it?
 
Re: Fault finding - perplexed - FIXED !!!!!!!!!!!!!!!!!

My neighbour hacked at his nice newly plastered wall and this is what we found:

lee nail.jpg

The nail was touching the live and nothing else. I am of the opinion that the wall had been "wetter", conducted to the closest back box, and thus why at first the tripping had started but latterly hadn't.

Nice new bit of cable installed - tested OK

Got to deliver my bill next - not sure how that will go down!
 
Last edited by a moderator:
Nice - sounds a nice head scratcher !! This is why i'm so glad I dont do any domestic work :)

I was going to suggest trying to locate the nail heads in the skirting if at all possible, clean a spot for test leads and test continuity between nail head(s) and conductors, that way after exhausting splitting rings etc you would have had proof a nail had nicked the wiring ?
 

Reply to Fault finding - perplexed - help!!! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
202
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
749
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top