philly4321
Hi All,
Been out to a job last week as the RCD was tripping. Narrowed this down to the ring main circuit. The house is a three bedroom house with only one ring main servicing the entire house.
Continuity test on ring are within parameters - L-L - 0.56 N-N - 0.58 E-E - 0.94
I then put the circuit on the non RCD side and it energised fine no issues, Zs tests on sockets were also fine.
I then undertook an IR test and the results were 0.00 for L-N, L-E & N-E, I have never come across this before and has left me puzzled. All tests undertaken using Megger 1552 MFT.
The house has been rewired by a keen amatuer at some stage and I believe the problem lies in one of the numerous spurs off the ring.
I am going to be relacing the consumer unit as it has seen better days, RCD ramp test was only 15mA, however with the readings on the IR test I am stumped. I have taken off all socket faces and checked cabling and all is well behind sockets.
Usual suspects such as any DIY, nails for picture etc have been ruled out. Dishwasher was causing problems about 6 moths ago on hot wash only but this seems to have been rectified.
Going back tomorrow and will split each socket and spur in turn to see if I can locate fault, but at moment feels like im stabbing in the dark. House covered in laminate flooring top to bottom with anice shiny fitted kitchen, so minimum disruption is a neccsisty.
Any guidance or similar experiences would be most welcome.
Thanks
Been out to a job last week as the RCD was tripping. Narrowed this down to the ring main circuit. The house is a three bedroom house with only one ring main servicing the entire house.
Continuity test on ring are within parameters - L-L - 0.56 N-N - 0.58 E-E - 0.94
I then put the circuit on the non RCD side and it energised fine no issues, Zs tests on sockets were also fine.
I then undertook an IR test and the results were 0.00 for L-N, L-E & N-E, I have never come across this before and has left me puzzled. All tests undertaken using Megger 1552 MFT.
The house has been rewired by a keen amatuer at some stage and I believe the problem lies in one of the numerous spurs off the ring.
I am going to be relacing the consumer unit as it has seen better days, RCD ramp test was only 15mA, however with the readings on the IR test I am stumped. I have taken off all socket faces and checked cabling and all is well behind sockets.
Usual suspects such as any DIY, nails for picture etc have been ruled out. Dishwasher was causing problems about 6 moths ago on hot wash only but this seems to have been rectified.
Going back tomorrow and will split each socket and spur in turn to see if I can locate fault, but at moment feels like im stabbing in the dark. House covered in laminate flooring top to bottom with anice shiny fitted kitchen, so minimum disruption is a neccsisty.
Any guidance or similar experiences would be most welcome.
Thanks