I find fault finding a methodical process, I will however find it very rewarding once problem is found. The other factor that I find confusing is that no work has been completed at the property so causes of the problem have got to be something environmental
 
I had an IR reading of "0" bet L & N. Opened up two FCU's on the ring with neons, cleaned and checked for gremlins, put back and the reading came up with 469 meg ohms.
 
The fact that you have 0 between N and E AND L and E leads me to think it may well be a trapped cable that has pierced all 3 cores....or, as said before, water in a junction box. This is not just a N to E fault as your meter has revealed.
 
Sockets in kitchen cupboards seem to be a favorite on all my fault finding jobs, or hidden sockets behind an appliance.

Had one last week, RCBO kept tripping out. I started by asking the home owner what they were using when it tripped. A lawn mower, so started and removed that socket to find it faulty.
 
had a good one yesterday in a factory unit. lost all sockets. located fault on socket ring there was a picture hanging on a nail which had peirced line-earth and on top of that a nail holding suspended ceiling edging up which had peirced neutral-earth. both these nails had been in place for at least 12 months!!!! why the rcd had not tripped before is baffling me, after repairs were made rcd tripping times I/R etc all ok.
forgot to say the cables were feeding a socket in a w/c hidden behind the cistern....!!!!
some plumbers really need to hire a brain before plodding off to work.
 
Last edited by a moderator:
Yesterday went to a school with floor lights in a canteen area. We only installed them six weeks and already tripping out. 
There's 13 lights and they are all encased in the floor so once I locate the specific one I'm going to have great fun telling them it's coming out. 
IR tests where showing ok, not brilliant for cable installed six weeks ago but passable and continuity was going bonkers with 8890 ohms!!!! Sounds like water damage somewhere.
 

Reply to Fault Finding Problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
685
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top