Helped a friend out today, downstairs sockets randomly tripped during the night and now won't stay on. I narrowed it down to an earth fault on a leg between 2 sockets in the back room.
The cable dissapears under the floorboards and the room is laminated. I explained the situation and my friend was very against having to rip it out and replace it.
I suggested making 2x A2 radial circuits out of the RFC and making that leg redundant. Obviously that means 2x 20A MCB's to replace the 32A.
My friend was more than happy to do this, however it feels like a bodge and I'd be more happier to replace that leg.
Not really looking for advice, I guess I'm just sharing my experiences.
In this case, the customer (owner) of the installation has the end say on work, so long as it complies and is safe.
I did manage to do some checks on the circuit before leaving. Zs is good, RCD times are good and IRT were good.
The cable dissapears under the floorboards and the room is laminated. I explained the situation and my friend was very against having to rip it out and replace it.
I suggested making 2x A2 radial circuits out of the RFC and making that leg redundant. Obviously that means 2x 20A MCB's to replace the 32A.
My friend was more than happy to do this, however it feels like a bodge and I'd be more happier to replace that leg.
Not really looking for advice, I guess I'm just sharing my experiences.
In this case, the customer (owner) of the installation has the end say on work, so long as it complies and is safe.
I did manage to do some checks on the circuit before leaving. Zs is good, RCD times are good and IRT were good.