Done a condition report on a old mains board, everything good apart from ring final, got 0.55 nn 33.7ll and 3.8 on ee, changed board to main switch and rcbos, carried out a full accessory swap on all sockets and fuse spares in house, found some bad practice, twisted lives, n and earth's, no sleeving all things to add to the high resistance problem. Retested board end to end 0.55nn 0.90 ee open ll. So changed the 32 rcbo to 2x16a rcbos broke the ring in half having 5 sockets on one side and 6 on the other. Rcbo trips! Any idea what I'm doing wrong?

I know the information isn't details but fire away with questions.

Help ?
 
I think you first need to confirm exactly what is connected to what.
Draw the circuit out and it may well become apparent
 
Most likely there is some link between what you think are now two separate radials, and probably one RCBO is tripping faster than the other.

But hopefully if you can go back and do a more thorough check of the extent of L & N on each circuit you will find the problem. Also worth verifying there is proper isolation of L & N to all other circuits and to CPC/Earth.
 
Thanks for all the help guys, outcome was that the ring had a dead short N-E from the lounge to the kitchen.
I took all the sockets off and disconnected all connections at the board, identified and mapped the wiring by way of continuity. I then was left with two unidentified cables between two sockets. I done a IR on this leg and had a connection between N&E. Left this leg disconnected. Reconnected all other sockets splitting the ring into two radials. Unfortunately the client lost a socket rom 1 side of the radial but i managed to get a full test. ?? Thanks for the advice and help.
 
Last edited:

Reply to Fault finding ring final RCBO in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top