Fault finding simulators for AM2 trainee | on ElectriciansForums
Discuss Fault finding simulators for AM2 trainee in the Electrical Course Trainees Only area at ElectriciansForums.net
Doncaster, South Yorkshire
Hey, I am currently doing the AM2 but finding it difficult to find anything relating to fault finding well anything with any substance. I was wondering if anyone has come across any fault finding/trouble shooting software that can help me get to grips with the principles. Thanks for your time.
To be honest I don’t think such a thing exists. What do you know about fault finding so far? I am unfamiliar with the AM2 but it shouldn’t be much different from the FICA up here so the common faults you’d be looking for would be things like; reversed polarity, incorrect phase rotation, short circuits, earth faults, low insulation resistance, high CPC resistance, connections which are missing or have “fallen out”
On the AM2 you just get a multimeter to use. There is a composite installation lighting, sockets, CH and solar, motor starter, fire alarm etc and you need to give the type of fault, Its location and rectification method.
I know about the half split method thats fine on radials but I just get a bit confused when it comes to more complicated circuit like the CH/ solar and the motor starter curcuit
I was lead to believe you only have access to a multimeter for the fault finding, but that wasn't the case (the AM2 documentation states that one of the intentions of the fault finding section is to ensure you are capable of using the most appropriate equipment). I had access to an AVI, an MFT, a phase rotation indicator and a data cable tester.
So if you've got a fault that reads "Problems were experienced taking insulation measurements", an insulation resistance tester is the most appropriate tool (I used the insulation test on an MFT for several faults).
You should remember that there are only certain types of faults... open circuit, short circuit, high resistance connection and mis-connection. So even if you do only have a multimeter available, you can identify these using the continuity (resistance) mode.
  • Open circuit = No reading
  • Short circuit = 0 (zero) reading
  • High resistance = Reading above a few ohms
  • Mis-connection = Continuity (0 or very low reading) between incorrect conductors (e.g. between L1/L2 at one end and L2/L1 at another with no connection between L1 and L2 at one end)
With regards to testing the heating system, you just need to think logically about it and learn a little about how the components work, like the connections on a motorised valve for example and what they do (Blue = Neutral to motor, Green/Yellow = Earth if present, Brown = Line to motor, Grey = Line to switch, Orange = Switched line return - So, to activate the valve the brown is connected to line, the motor runs up, opens the valve and at the end of travel closes the switch connecting Grey and Orange which will typically supply power to the demand input on the boiler/pump to engage the burners and start circulation).
So if for example you have a fault that suggests the heating circuit MCB trips when the heating program comes on, it's possibly a short circuit between line and neutral or line and earth on one of the components involved in that (room stat, programmer connections involved in heating, motorised valve, boiler and circulator). Just work through it logically one component at a time using the wiring diagram.
Hope this helps.
Thanks Chick I did the exam a few weeks ago and failed the fault finding I only had a multimeter. Like you say I've just got to take my time and work thru methodically. I have heard someone mention it may be changing early next year so you have to do steel conduit bends etc don't know how true this is.
Yes, I've heard the same that containment and tray work is coming back into it.
I find it quite interesting that you only had access to a multimeter because that's hardly a fair and true assessment of competence under real life conditions. The only time I've used my multimeter for fault finding is when I've been working on alarm panels and even then it's only been to confirm whether my Fluke T150 is telling me the truth with low voltages.
Can you remember which faults you had and what you put down?
No to be honest I didn't have a clue I know I had a high resistance on one circuit and a cross connection on another. The instructor gave us the multi meter and told us most of the faults could be found using the continuity setting. So I just tried to go thru each circuit from the board to the end of the circuit on continuity setting. I don't get to use multi meters at work so it kinda thru me. Theres not much info around that shows you a tried and tested method. I guess this is where experience comes in and when you have to think on your feet.
Reply to Fault finding simulators for AM2 trainee in the Electrical Course Trainees Only area at ElectriciansForums.net
It maybe a case of the display has died, especially if the unit is actually working, but as James has said you could be opening a can of worms...
Hi all, I’m in the final stage of my electrical apprenticeship and I need some help to complete my portfolio. I have all units apart from 115...