Hi all & thanks in advance for the time.

I'm due on Monday to complete my trade test. (FICA IN SCOTLAND) The part of my test i am to undertake is Fault Finding and rectification. For the test i will be put in a booth by the assessor and issued a job card that briefly describes the circumstances of the fault Eg; the light is iinoperable. From this information & by using only a markingdale continuity Buzzer i need to find out the location of the fault and the type of fault Eg; open circuit on live conductor between switch and light, rewire length of cable.

So can anyone give me any other examples of how you would locate a fault using only a Martindale Continuity meter and how you would rectify said fault? I will attach a photo of the continuity tester as it is very basic.

Thanks once again.
 
I think you would wise to draw the circuit out now, before you have your assessment. Think about how each point should either be connected or not conected with each other point. Then, at your assessment, first ensure the circuit is complete, ie. no open circuits. Then check nothing is shorted together that shouldn't be, ie. no short circuits.
 
Your assessor will be looking for you to find the fault and rectify BEFORE energising the circuit. The breaker tripping or not is not used a satisfactory method of successful fault finding.

I believe the lighting is a 2-way circuit? Its been a long time since I did my FICA.
Someone correct me here, bu. He wont ask you to rewire it physically, but simply for you to tell him what the problem is, and where it is likely to be.

You just need to understand which conductors should give continuity, and which shouldn't. Figure out what you need for it to work regarding live, switchwire and neutral, and/or strappers (pass wires, whatever you call them)
Remove the lamp, as it will show as a live to neutral short circuit and lead to possible confusion.
J remember when I was doing my AM2 the assessor flicked the switch. The continuity tester sort of bleeped quieter than it should have.

I put this down as a high resistance joint.

There was a fault on his simulator switch. We agreed it was open circuit
 
Your assessor will be looking for you to find the fault and rectify BEFORE energising the circuit. The breaker tripping or not is not used a satisfactory method of successful fault finding.

I believe the lighting is a 2-way circuit? Its been a long time since I did my FICA.
Someone correct me here, bu. He wont ask you to rewire it physically, but simply for you to tell him what the problem is, and where it is likely to be.

You just need to understand which conductors should give continuity, and which shouldn't. Figure out what you need for it to work regarding live, switchwire and neutral, and/or strappers (pass wires, whatever you call them)
Remove the lamp, as it will show as a live to neutral short circuit and lead to possible confusion.
J remember when I was doing my AM2 the assessor flicked the switch. The continuity tester sort of bleeped quieter than it should have.

I put this down as a high resistance joint.

There was a fault on his simulator switch. We agreed it was open circuit
 
Really important that you understand what the four possible faults are (see my earlier post).

There is only one fault per card.

The faults are ALL wiring faults (not things like a broken switch, faulty lamp etc).

So for example - a three phase motor runs, but not smoothly. What does this suggest? A loss of one phase? So, test continuity of each phase, from db to starter and from starter to motor box. Identify which phase and where fault lies. Your answer may be something like “ open circuit fault on L1 conductor between dB and starter; rewire L1 conductor between dB and starter; retest”.
 

Reply to FAULT FINDING USING CONTINUITY TESTER ONLY in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
Great, then I am a bit bemused why you posted your original question. You need to stop doing any work that you cannot properly test, safety is...
Replies
12
Views
1K
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
681

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top