Eddiesparks

Did a board change today and put in rcbos for mcbs in common areas of a block of flats. Meggered out ok before i started by the way!!

Rcbo for outside lights didnt hold. Mcb was fine before. All others held fine. So neutral to earth fault right? Also disconnected neutral from rcbo no problems til neutral connected, with live connected all good. Connected neutral trip. Connected just neutral - trip. Earth in all the time.

Disconnected that circuit's earth and functional earth to see if it would hold. No joy. Traced earth and it goes nowhere, cut off at contactor! However outside lights gave me a Zs so earth must be taken off another circuit.

Thought about borrowed neutrals - but all other rcbo's held - didnt trip in a pair. Also meggered between neutrals came out ok. Even disconnected all other neutrals except outside lights. No joy.

It's a main board in common areas that feeds that building's power and lights and outside lights plus feeds a few submains. Flats are on separate main incomer individual fuses. Could it be a borrowed neutral from a lighting circuit in one of the flats.

Also, old board had charring round where the main neutral from 100a switch meets neutral bar. Is this probably unrelated and due to bad connection??

What a horrible day. Going back tomorrow to fault find some more. But it's hard to find the ordering of the outside lights there are groups of them all over the place. I suppose get Zs on all of them and lowest is closest to the board.

Wish me luck, but more importantly some highly experienced insight would be great!!
 
Boydy. Contactor is controlled by external PIR. Disconnected that and still fault. I'm there now. Lots of food for thought lads. Thank you. I'll get cracking! Ps def not L-E high resistance fault because fine with live connected. Introducing the neutral brings all the problems. I am doing what baldsparkies said and disconnecting neutrals bit by bit. I have a suspicion where roughly fault may be...
 
Boydy. Contactor is controlled by external PIR. Disconnected that and still fault. I'm there now. Lots of food for thought lads. Thank you. I'll get cracking! Ps def not L-E high resistance fault because fine with live connected. Introducing the neutral brings all the problems. I am doing what baldsparkies said and disconnecting neutrals bit by bit. I have a suspicion where roughly fault may be...

Good luck eddie let us know how you get on im intrigued!!
 
Surely when testing for borrowed neutrals you don't test between neutrals? Surely the live of one circuit against neutrals of all other circuits, neutral to neutral shows only interconnection between neutrals
 
Testing between neutrals would work so long as everything is on as there would be a connection through the faulty load and one of the OK loads to give the reading, but from line to another neutral would only be testing through the faulty load so gives a chance for diagnosis.
However if the load is electronic and near infinite resistance it may not show up.

This is my thought:
[ElectriciansForums.net] Fault has stumped me!!
be interested in feedback.
 
Testing between neutrals would work so long as everything is on as there would be a connection through the faulty load and one of the OK loads to give the reading, but from line to another neutral would only be testing through the faulty load so gives a chance for diagnosis.
However if the load is electronic and near infinite resistance it may not show up.


This is my thought:
View attachment 23537
be interested in feedback.

That makes perfect sense to me and the drawing makes it even easier to understand. Thanks mate
 
I would try and trace with earth leakage clamp meter with an MCB in for now, and trace it through with just that 1 circuit live then liven up other circuits and see what happens with the readings , you could try with lamps in first and all switches off , then try with switches on one at a time , trace it that way ,
 

Reply to Fault has stumped me!! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
775
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top