110v from switch to switch (see attached picture), tn-cs system with 30mA RCD in Place, trips fine when tested at 100% and 500% customer complained of getting shocked when touching both switches at once but doesn’t trip with this fault, have a few theories, but any suggestions?

514258D2-9701-4C38-8195-170B5A64DE7A.jpeg
 
Dont suppose you have drummond tester with resistance injector?

Is that one of these?
3-000-024-A.jpg
 
Is that a new house, or newly refurbished, judging by the woodwork?

Get Kev the builders mate to tell you exactly what he did or didn't do when he "rewired" and put new accessories on.
 
I had similar ages ago, customer getting intermittent tingles from metal dimmer switch, no voltage between plate & known earth mind.

I left her to fry, whilst consulting members here (nahh not really, swapped switch to plastic). Went back to investigate with new advice and found there was no continuity between installed switch cpc & earth terminal in CU.

I wasn't taking the Michael out of the OP by the way :)
 

Reply to the thread, titled "Fault on domestic home wiring" which is posted in Domestic Electrician Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top