It's been a few years since college and I'm stuck on understanding this,

I'm getting an intermittent fault on kitchen sockets. Causing some tripping.

Broken it down and when I IR test the circuit. L to E is 200+
N to E is 200+
But when I test N&L to E thruster fluctuates between 120Mohnm to 160Mohm

I don't understand why it's over 200 M when I test separately.

Can anyone explain to my stupid brain please. TA
 
fault on N&L to CPC

Definitely not an appliance. Thanks big cheese that explains the reading. It's now dropping down to 30Mohm now and again.

So how can I trace intermittent faults without rewiring everything?
 
if the circuit is a ring. guesstimate the mid point and split it. then you may well find a low reading on 1 leg. then split that leg again.... and so on till you narrow it down. even so, 30Meg. will not trip a RCD.
 
fault on N&L to CPC

Spent hours doing that. I get 200+ on leg L&N to E then 10mins later back to below 100Mohm.

I'm worried about the fault to other causing problems to the ladies appliances.
 
Have you taken the sockets off the wall? Is anything damp / newly plastered / decorated? How old is the install? 30M should be findable and I personally would look for it because it could direct you to the site of cable damage etc; a short length of T+E and a few fittings should be able to get over 30M. But 100M... a few years ago your tester wouldn't have been able to read that high. I wouldn't exactly call it a fault and it wouldn't cause any other problems.
 
fault on N&L to CPC

Well I've put all sockets back on and it's reading 200M+ L&N combined. Don't know why. Maybe fiddling with sockets?? Who cares I'm walking away now :)
 
Re: fault on N&L to CPC

Well I've put all sockets back on and it's reading 200M+ L&N combined. Don't know why. Maybe fiddling with sockets?? Who cares I'm walking away now :)

That's that one sorted then! Ermmm....... Daz
 
could have been a cable caught up by a screw or squashed against the back box. by pulling the faceplate off and refitting, you could have cleared the fault.
 
Damp maybe a prime suspect on this one, or the old bottle sterilizer right next to socket or kettle etc . U could remove all sockets and connector block the ring and test cable only. Just s thought!
 

Reply to fault on N&L to CPC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
652
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
736

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top