Been called to a fault today customer saying RCD tripping when under load.

I go rcd holds in till he plugs something in that say uses more that 50w, I try and ramp test rcd - no trip, 5x no trip, 1x no trip, rcd test bottom - no trip. so I think it’s a faulty rcd, i put a new rcd in and test again 5x no trip, 1x no trip, rcd test bottom - no trip same thing again as soon as he plugs something with some load in it trips the new rcd out.

I look in to it a bit deeper IR on all circuits >20M.

I then disconnect the main earth from the PME, everything is then fine, RCD trips correctly and stays on under load, I've now decide it's done to the DNO so out comes western power they that one look and say nope it’s on your side it must be a faulty appliance.

In the mean time I’ve replaced the consumer units Main switch with an RCD due to the property having unstable earth.

Any ideas as to where i can go from here as it’s something I’ve never came across before?
 
Well the op said he was called out to a fault
so it has been working
hes changed the main switch
DNO saying nowt to do with them
no new meter
hes done ir on circuits and all >20Meg
Im thinking it's an appliance that's started to Cause this problem it's the freezer with the lead pipe in the kitchen lol
 
Might be worth checking the configuration of the main neutrals in the CU. I had one awhile ago where a friend asked me to check out a CU his son had installed ( an apprentice ), and he had the Neutrals configured incorrectly in the Board, with so many configurations possible these days its easy to get one wrong and to miss it when you look at the Board. Everything worked fine until an appliance was plugged in and then the Board tripped!

Regards.
 
check any appliance on a fused spur, got a simliar problem recently in a static caravan and after a few hours got it down to a trapped flex at back of built in gas oven, plumber out to remove appliance then repair and plumber to refit oven!!
 
Might be worth checking the configuration of the main neutrals in the CU. I had one awhile ago where a friend asked me to check out a CU his son had installed ( an apprentice ), and he had the Neutrals configured incorrectly in the Board, with so many configurations possible these days its easy to get one wrong and to miss it when you look at the Board. Everything worked fine until an appliance was plugged in and then the Board tripped!

Regards.


Same thing happened to me and my partner few weeks ago.. After trying to look too deeply into it the matter we found it was right in front of our eyes.. Silly mistake, yapping about one thing an another distracted us from the obvious.. Check the neutrals.. :blush5:
 

Reply to Fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
685
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top