Hello just had quick look at the fault on the way home last night as I was passing by. Basically the up sockets are on a rcbo it's a bit strange because when ever you plug some thing in like a battery charger for a drill or a power tool it does not trip. But when plugging in a heater it trip straight away. Didn't have my megger with me so didn't carry out any test as of yet, any one seen that before.
I swapped the rcbo over with a new one and still happened. I will run a ramp test to see it trips when I return along with the basic ir and r1+r2 tests.
I have seen it before when polarity has been reversed in a socket when energising a load the Rcd will trip.
I swapped the rcbo over with a new one and still happened. I will run a ramp test to see it trips when I return along with the basic ir and r1+r2 tests.
I have seen it before when polarity has been reversed in a socket when energising a load the Rcd will trip.