Customer wants two 2.5kw heaters which are fed via a dedicated curcuits and protected by15amp mcb's sockets changed as another electrician said they need to be on 13amp fcu's and not 20amp double pole switches.

Is he correct and would you replace and charge?
 
15 amp mcb's? Are they old wylex type replacements.
If the heaters are supplied with 13 amp plugs IMO I would use fcu's in order to maintain manufacturers 13 amp requirement.
 
15 amp mcb's? Are they old wylex type replacements.
If the heaters are supplied with 13 amp plugs IMO I would use fcu's in order to maintain manufacturers 13 amp requirement.

if appliances are supplied with 13amp plugs-you may have to leave them on:)

for warranty purposes

only recently i stopped chopping them off-mind you:o
 
standard practice...15/16a radial through DP switch....FCU?...why?

Some people fit 13amp fcu for storage heater 2.5kw and below and 20amp dp for the bigger 3.4kw although in this instance i think the spark doing the work for there extension was trying to get more work perhaps
 

Reply to the thread, titled "fcu and 20amp dp" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top