P
peterb2428
Customer wants two 2.5kw heaters which are fed via a dedicated curcuits and protected by15amp mcb's sockets changed as another electrician said they need to be on 13amp fcu's and not 20amp double pole switches.
Is he correct and would you replace and charge?
15 amp mcb's? Are they old wylex type replacements.
If the heaters are supplied with 13 amp plugs IMO I would use fcu's in order to maintain manufacturers 13 amp requirement.
if appliances are supplied with 13amp plugs-you may have to leave them on:)
for warranty purposes
only recently i stopped chopping them off-mind you:o
standard practice...15/16a radial through DP switch....FCU?...why?
Some people fit 13amp fcu for storage heater 2.5kw and below and 20amp dp for the bigger 3.4kw although in this instance i think the spark doing the work for there extension was trying to get more work perhaps
fcu and 20amp dp
Australia
peterb2428,
peterb2428,
TrueNAS JBOD Storage Server