View the thread, titled "FCU, bathroom light" which is posted in Australia on Electricians Forums.

N

nick182

hey guys,,

ive been asked to wire this bathroom light to an existing FCU for a friend and it turns out that i cant use that FCU.. so would i wire an FCU from an existing socket outlet to the FCU then to the switch? i have looked through all of my books but cant pin point an answer. Im a little concerned as the bathroom is upstairs and so is the socket outlet (which is not protected by an rcd.) The manufacturers instructions are pretty much useless. http://www.heatnlight.co.uk/S451_IB.pdf



I have a lot of idea's as to how i should wire this up but im sure that im missing out on something....
any insight would be of great help

thanks...


Nick
 
What is the loading on the unit ? Often you can come of the existing lighting circuit with these small bathroom type heaters, via an FCU
 
Last edited by a moderator:
As this has a heating element,if coming from the lights you would need to assess the loading of the circuit.
There is no reason why you couldnt feed it from the ring through an RCD FCU....via a pullswitch.
 
No Nick that would mean that it is just the socket that is RCD protected, not any part of the circuit.

I normally would either try and fit an RCBO for the entire lighting circuit, which in many cases you can't I agree, especially on a rewireable BS 3036 board.

Or fit a stand alone enclosure fed from the existing CU lighting way, and divert the lighting circuit into the enclosure that would have the RCD.

A third way would be to fit an RCD spur into the loop that enters the bathroom lights. I don't personally like that as I feel the regs tell us that the circuits controlling the bathroom needs protecting, but there is an argument that it does not mean that.
 
Malcolm's ideas are the best and the caveats.

The unit seems to be taking about 3.5A so could be wired into the lighting circuit via an FCU, depending on the loading on the rest of the lighting circuit but this does not address RCD protection.
The easiest way to progress would be to take an RCD FCU off the nearby socket circuit and wire the heater into that, take away the lighting circuit currently supplying the bathroom light.
In this way the circuit you have installed in the bathroom is RCD protected, however similarly to what Malcolm says this may then be modifying the socket circuit that should have RCD protection over the whole circuit!
 
looks like i have to notify LABC on this one and issue a minor works.... why does a simple job have to become so rediciously expensive? Arfgggh

thanks guys... if i have any more questions i might hassle you guys later on.

wish me luck
 
what if i were to use a double pole pull chord switch? would that suit the requirements instead of getting the LABC involved and having the customer pay through the nose...?
 
looks like i have to notify LABC on this one and issue a minor works.... why does a simple job have to become so rediciously expensive? Arfgggh

Try this, how much to install a £5.00 coach light that has already been secured to the wall of the games room at the bottom of the garden. Cable just needs to be sent through wall and wired into switch?

Oh, no RCD protection anywhere and no bonding to Gas or Water lol

My quote £230.00 Their answser? I think not lol
 
Try this, how much to install a £5.00 coach light that has already been secured to the wall of the games room at the bottom of the garden. Cable just needs to be sent through wall and wired into switch?

Oh, no RCD protection anywhere and no bonding to Gas or Water lol

My quote £230.00 Their answser? I think not lol

And that's where Mr DIY kicks in and rather that have peace of mind that their electrical installation has been brought up to a safer standard they'll opt to do the work themselves and "save" their £230!
 
And just to be contriversal why would fixing a light on the outside wall of a house/outbuilding have any affect on the lack of water/gas bonding. Some of these regs are just plain daft and homeowners can see that.

Now if the homeowner wants extra sockets in the hose that's another matter.
 

Reply to the thread, titled "FCU, bathroom light" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top