FCUs as circuit protection for part of circuit | on ElectriciansForums

Discuss FCUs as circuit protection for part of circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Dunc

-
Joined
Mar 18, 2011
Messages
532
Reaction score
153
I'm sure we've all come across these scenarios:

16A supply to garage from consumer unit to a socket and an FCU feeding the lights with a 5A BS1362 fuse.

32A ringmain extended to feed conservatory with FCU with 3A BS1362 fuse feeding garden/patio lighting.

Central heating supply from ringmain or dedicated 16A circuit, all controls fed in 1mm PVC-PVC flat cable via FCU with 3A BS1362 fuse.

Now my question is, how do you go about doing the testing and recording the results on a minor works certificate considering the FCU alters the supply characteristics of the final circuit. Do you provide separate R1+R2 and Zs reading for everything after the FCU, do you test to the furthest point on the circuit and record it as if the FCU doesn't exist or do you just test at the FCU as though that is the final point and disregard everything there after. Or, do you do something else entirely?

Would be interested to know what you do.
 
Last edited:
Agree with spin there I would note it as a sub circuit within a circuit and over 2 lines.

Of course if your Ring final is RCD/RCBO protected and the spur is just a normal FCU then really the FCU EFLI for that 1362 fuse is pretty much negated, and would just enter 1667 in the appropiate box. The 3amp 1362 is just there for overload protection on that sub circuit.

If it was the other way round the FCU was RCD protected and the ring final was BS 3036 or MCB protected then I would enter over 2 lines the recorded Zs value for the ring final and then 1667 for the sub circuit.
 

Reply to FCUs as circuit protection for part of circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top