Its been along day, I've just finished off with looking around a big garden which has all sorts of electrical things going and would appreciate a bit of advice on VD.
Garden is supplied by 2.5mm SWA (buried), at present taking about 1000W from a 20A MCB in the garage CU. The chap wants 2 greenhouse fan heaters installed. The run is about 40m's in total.
Max allowable VD = 11.5
VD (mV/A/m) for 2.5mm = 18
length = 40m
so available power = (max allowable VD x 1000)/length x VD
= 16A (approx) = 3680W
Garden is already taking 1000W so I'm left with 2680W for 2 greenhouse fan heaters.
I have 2 questions:
1. Can anyone see a half decent greenhouse fan heater that is only 1.3kW?
2. Really, Really tired and just cant figure out if VD means the cable will be unsafe or the MCB more likely to trip.... ridiculous question I know but I've had a glass of port (yeah I'm ready for the jip :rolleyes2, I'm tired and I just want to figure it out. Quote doesn't even need to be done for a week!
Garden is supplied by 2.5mm SWA (buried), at present taking about 1000W from a 20A MCB in the garage CU. The chap wants 2 greenhouse fan heaters installed. The run is about 40m's in total.
Max allowable VD = 11.5
VD (mV/A/m) for 2.5mm = 18
length = 40m
so available power = (max allowable VD x 1000)/length x VD
= 16A (approx) = 3680W
Garden is already taking 1000W so I'm left with 2680W for 2 greenhouse fan heaters.
I have 2 questions:
1. Can anyone see a half decent greenhouse fan heater that is only 1.3kW?
2. Really, Really tired and just cant figure out if VD means the cable will be unsafe or the MCB more likely to trip.... ridiculous question I know but I've had a glass of port (yeah I'm ready for the jip :rolleyes2, I'm tired and I just want to figure it out. Quote doesn't even need to be done for a week!