As Dave indicates above, any size of power source to which you hook up will constitute a temporary electrical system, however BS7909 treats systems up to 6kVA as "small/simple" with the main difference being the level of testing and therefore competence required. Essentially, many end users will be able to demonstrate sufficient and suitable competence to manage a small/simple event and testing the RCD.
Above 6kVA, the testing required by BS7909 is more complex and outside the remit of most end users. A good understanding of BS7671 and an MFT are required to carry out the testing, which is why events have a dedicated person doing the power, so you can simply say "give me 32A" and then concentrate on cooking!