Feed and switch wire at an intermediate... | Page 2 | on ElectriciansForums

Discuss Feed and switch wire at an intermediate... in the UK Electrical Forum area at ElectriciansForums.net

TJC1

-
Joined
Feb 23, 2014
Messages
167
Reaction score
7
Location
United Kingdom
Evening all

Try to rack my brain about whether this would work.....

Customer on a job wants to add a 3rd switch on a lighting circuit, however it is near impossible to get from the 2way switch but easy to get from the first switch

Will having the intermediate switch where the feed and switch wire work.....

Cheers

T
 
@theshaniqua crude edit....
[ElectriciansForums.net] Feed and switch wire at an intermediate...
 
It's still wrong. PL and SL must tap into the brown and grey of the same strapper cable. Imagine they were paralelled at one of the 2-ways, and then just transferred to the other end of the same strapper cable.
 
Yes. I think manufacturers are inconsistent with labelleling L1 and L2 on intermediates. Traditionally I recall it being L1 for both 'brown' terminals and L2 for both 'grey', but have seen drawings as per yours with L1 for both terminals facing one 2-way and L2 for both facing the other. Perhaps someone could confirm? I don't usually install light switches so it's ages sinnce I looked at one.
 
Yes. I think manufacturers are inconsistent with labelleling L1 and L2 on intermediates. Traditionally I recall it being L1 for both 'brown' terminals and L2 for both 'grey', but have seen drawings as per yours with L1 for both terminals facing one 2-way and L2 for both facing the other. Perhaps someone could confirm? I don't usually install light switches so it's ages sinnce I looked at one.
You're right, they do vary from manufacturer
 
You're right, they do vary from manufacturer
They certainly do. More or less any combination you like ?
The common theme seems to be a terminal at the top gets connected to one or other at the bottom ?
(as you might imagine from the construction of the thing). Amongst others Schneider go for L1, L2, L3, L4
 

Attachments

  • [ElectriciansForums.net] Feed and switch wire at an intermediate...
    04EC4DED-4948-4B28-BC1B-F90CE56DD6B6.jpeg
    81.4 KB · Views: 43
  • [ElectriciansForums.net] Feed and switch wire at an intermediate...
    433B9BFF-7A33-4648-8D62-7759C7DAE8A7.jpeg
    41.1 KB · Views: 36
  • [ElectriciansForums.net] Feed and switch wire at an intermediate...
    368F2568-BF8F-4F76-9957-7A14F970B487.jpeg
    61.1 KB · Views: 38

Reply to Feed and switch wire at an intermediate... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Firstly I would suggest that of the three sets of cables, they are not all 'incoming'. There might be one cable (of 3 wires) bringing in permanent...
Replies
1
Views
759
Back to the Men's Shed today to complete the installation of the 4 LED battens in the attic. These were a joy to fit, having screwed the units to...
    • Like
Replies
0
Views
164

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top