If you have the space in your existing CU then fit an RCBO
If you run the garage from an existing board fitted with an RCD then a problem in the garage would cause problems with other circuits in the house being tripped. By running from an RCBO then the house would be unaffected.
Yes it would, just as would using an MCB at the house.
The difference being, that if anything in the garage caused the RCBO to trip, you would have to go back to the house to re-set.
Using an MCB in the house, and an RCBO in the garage CU would allow you to re-set without having to go to the house.
why does an swa have to be rcd protected if on a tt supplya distribution circuit should not be on a rcbo or rcd (unless tt system)
with an swa the armourings must be earthed and there you have your protected cable. rcd dist board in garage.
not sure what all the fuss is about?
I'm sorry but i cant see the problem and why this contravenes 314.
why does an swa have to be rcd protected if on a tt supply![]()
Quite simple, 314.1i) requires us to minimise inconvenience in the event of a fault.
What is more convenient, re-setting an RCD in the garage, or re-setting an RCD in the house.
why does an swa have to be rcd protected if on a tt supply![]()
a distribution circuit should not be on a rcbo or rcd