If you have the space in your existing CU then fit an RCBO, run SWA underground not forgetting to earth the armour at the supply CU. A CU with main switch and relevent MCB's will then suffice in the garage.

You will obviously need to do the relevent tests on the submain as well as the individual circuits within the garage.
 
If you have the space in your existing CU then fit an RCBO

Why would you say this?
Is there a cost saving perhaps?
To do such would breach Regulations in BS7671, specifically 314.1 parts (i), (iii) and (iv).
 
If you run the garage from an existing board fitted with an RCD then a problem in the garage would cause problems with other circuits in the house being tripped. By running from an RCBO then the house would be unaffected.
 
If you run the garage from an existing board fitted with an RCD then a problem in the garage would cause problems with other circuits in the house being tripped. By running from an RCBO then the house would be unaffected.

Yes it would, just as would using an MCB at the house.
The difference being, that if anything in the garage caused the RCBO to trip, you would have to go back to the house to re-set.
Using an MCB in the house, and an RCBO in the garage CU would allow you to re-set without having to go to the house.
 
Yes it would, just as would using an MCB at the house.
The difference being, that if anything in the garage caused the RCBO to trip, you would have to go back to the house to re-set.
Using an MCB in the house, and an RCBO in the garage CU would allow you to re-set without having to go to the house.

I'm sorry but i cant see the problem and why this contravenes 314.
 
a distribution circuit should not be on a rcbo or rcd (unless tt system)
with an swa the armourings must be earthed and there you have your protected cable. rcd dist board in garage.
not sure what all the fuss is about?
 
a distribution circuit should not be on a rcbo or rcd (unless tt system)
with an swa the armourings must be earthed and there you have your protected cable. rcd dist board in garage.
not sure what all the fuss is about?
why does an swa have to be rcd protected if on a tt supply :o
 
I'm sorry but i cant see the problem and why this contravenes 314.

Quite simple, 314.1:(i) requires us to minimise inconvenience in the event of a fault.
What is more convenient, re-setting an RCD in the garage, or re-setting an RCD in the house.
 
Quite simple, 314.1:(i) requires us to minimise inconvenience in the event of a fault.
What is more convenient, re-setting an RCD in the garage, or re-setting an RCD in the house.

I think you are taking minimising inconvenience to the extreme there.

By fitting the RCBO at the CU and you are minimising the inconvenience to to dwelling. Which in my opinion is enough.
 
had my annual assessment today (niceic) and 1 of the jobs was like this.
16th split board in house with tt supply. 4mm 2 core swa on non rcd side to log cabin. 2 way rcd board in cabin. no mention of needing rcd protection on the sub main and its news to me too.
 
I would put in a henley block and split the supply. Shove your existing meter tails into it, and fit a metalclad switch fuse for the garage. Shove some new tails from henley block to switch fuse, then run the appropriate sized 3 core SWA out to the garage. in the garage fit a metalclad consumer unit. Depending on what your intentions in the garage are i would fit a consumer unit with a 100A DP isolator and RCBO's for the individual circuits, or a 100A 30mA RCD incommer and MCB,s for the circuits, its up to you really. By doing it this way the garage install will have no effect on the existing, and vice versa in the event of a problem.
There are other things to consider, but without seeing it i cant comment. But if you are going a fair way i would shove an earth spike in as well.

Cheers........Howard
 

Reply to the thread, titled "feed for a garage" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
feed for a garage
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
39

Thread Tags

Advert

Thread statistics

Created
IRB,
Last reply from
davies84,
Replies
39
Views
5,728

Advert

Back
Top