Hello, i wonder if anyone could help.I'm fitting a new oven in an extension thats being built. I've ripped the old oven out and the old feed. The new oven is a 2.4kw.What amp breaker would you use and what size cable.I was thinking 32 amp a friend said 40 amp would be better suited. Any info would be much appreciated guys!
 
Any cooking appliance rated over 2kW should have its own dedicated circuit from the CU.

In which case this would need a 16A MCB.

This work is also covered by Part P and must be notified to LABC.
 
Any cooking appliance rated over 2kW should have its own dedicated circuit from the CU.

In which case this would need a 16A MCB.

This work is also covered by Part P and must be notified to LABC.
I have'nt got my part p as a friend is going to ticket it for me, and the buildings inspector has been out and its all above board.Would u have it on a radial or ring ? Cheers for your help

sounds like a single oven to me 2400watts/230= 10.4 amps so could go on a plug top or wired via fused spur using a 13 amp fuse
Thanks mate !
 
Last edited by a moderator:
I have'nt got my part p as a friend is going to ticket it for me, and the buildings inspector has been out and its all above board.Would u have it on a radial or ring ? Cheers for your help

Thanks mate !

This is not a regulation only a guidance im sorry if you dont like my response dont ask if you dont want peoples opinions, this guidance is part of the 17th edition which unfortunatley i havent done yet i personally would look at the circuit and make my decision and would probably still put it on a plug top or spur depends on the job though!!!
 
I work in kitchens and most new ovens today only require a plug or a 13A fused spare as stated above but remeber if you conceal any plugs etc you must have a visible isolation point ie 13A switched fused spare same with any integrated appliances
 
Personally, I'd wire it in 4mm (radial) on a 16A mcb straight into a cooker point.

Who knows, you may upgrade to a larger cooker in the future?!
 
This is not a regulation only a guidance im sorry if you dont like my response dont ask if you dont want peoples opinions, this guidance is part of the 17th edition which unfortunatley i havent done yet i personally would look at the circuit and make my decision and would probably still put it on a plug top or spur depends on the job though!!!
Had a bad day mate ??? I thanked you for your reply.Where does it look like i dont want your opinion
 
I work in kitchens and most new ovens today only require a plug or a 13A fused spare as stated above but remeber if you conceal any plugs etc you must have a visible isolation point ie 13A switched fused spare same with any integrated appliances

Im all for making life easier, however, IDEALLY, any cooking appliance rated over 2kW SHOULD have its own dedicated radial circuit - P362 BS7671 - and not be connected to a RFC to prevent any part of the circuit from exceeding the C.C.C of the cable for long periods.

If a new circuit is being installed anyway, then id run a 6mm to a single socket for the oven, so that its future proof.
 
Im all for making life easier, however, IDEALLY, any cooking appliance rated over 2kW SHOULD have its own dedicated radial circuit - P362 BS7671 - and not be connected to a RFC to prevent any part of the circuit from exceeding the C.C.C of the cable for long periods.

If a new circuit is being installed anyway, then id run a 6mm to a single socket for the oven, so that its future proof.
Thanks jason.I have'nt got my part p so could you tell me if this would pass 17th and building regs ??
 
Thanks jason.I have'nt got my part p so could you tell me if this would pass 17th and building regs ??

It would pass provided the correct routes and various other factors are taken into consideration when the cable is being installed.

However, this must be notified to your LABC before work starts and, for a fee, will come and do the required tests etc to confirm it all complies.

Other than that, get in an electrician who can self certify to do the work.
 
no part P, no domestic installers scheme either.
I can register with NICIEC in England but not in Scotland
This is really a topic for a new thread
 

Reply to the thread, titled "Feed to new oven" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Feed to new oven
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
christian,
Last reply from
lionelmcc,
Replies
14
Views
14,850

Advert

Back
Top