Hi I am putting a Small 2 way CU in a shed to feed 3 x double sockets and 2 x florescent lights. The run from the Main CU is 30m

I am wiring it in conduit and I will be using 4mm singles to supply it with a 20A Breaker at the main, is this ok?

Many Thanks
 
Thank you for clearing that up robbo. How far is the lorry/shed from the main CU? Just wondering if 4mm will be adequate as you are feeding it from a 32A supply. Have you done the VD calcs?
Also, regarding the bonding, what spinlondon said.

The shed is just under 30m away from the main CU I have looked at table 4D1 Ref Method B and 4mm will carry 32A the voltage drop on that was 4.47% (10.5v) which is within the 5% drop allowed.
I can always Reduce this to 20A as there will never be that kind of power going through it, all he has in there is a chop saw, table saw and a few battery chargers and these will never all be being used at the same time.

I will do that with the bonding then and take a 10mm back to the MET

Many thanks
 
Have you allowed for the fact that your conduit cables are rated differently to your armoured in your calcs, plus did you say there will be several running together in the conduit, hence temperature factors? Just thinking aloud as it is an assessment job...
 
Have you allowed for the fact that your conduit cables are rated differently to your armoured in your calcs, plus did you say there will be several running together in the conduit, hence temperature factors? Just thinking aloud as it is an assessment job...

I hadn't no, thanks for pointing that out. i will use a 20A in the main CU.

Many thanks
 
I hadn't no, thanks for pointing that out. i will use a 20A in the main CU.

Many thanks

Which I was going to use in the first place as I thought it was a bit close but someone mentioned in one of the earlier posts that I could go 32A but they wouldn't have known to take the other factors into consideration either.

I bet you have quite a vivid image of this installation now :) thank you for all of your comments.
 

Reply to Feeding a Shed Cu from the main CU in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

BTW, the LD at the house will be 1" to accommodate the 6/3 coming from the house. Will use a 1" to 3/4" adapter to neck down to the 3/4" conduit...
Replies
1
Views
209
  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top