Hi guys,

I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a single socket for a freezer unit. I also have an additional 32 Amp (idle).
Now I have a log cabin 10m away. I am going to install a new consumner unit in the LogCabin and feed it from the 32 Amp MCB via a 4mm SWA cable. This Log cabin CU will have the same stuff (perhaps a 16Amp RCBO for 2 Radial sockets and a 6 Amp RCBO for lighting.


Regardless of it being notifiable etc , any suggestions objections are welcome.

Thanks!
 
I wouldn't notify a supply to a shed in my house why would I, and I am sure there are millions of sheds un notified in the UK, I get your point but I wouldn't bother myself and lets be honest there are many people in the uk who wouldn't bother either, it is a shed, not a kitchen, not a bathroom, not school classroom, a shed and owned by the OP, not him doing a job for someone else, so yes ok I am inappropriate, but honest
It is just because I used to live in Germany and I am used to abide by the law :) , or kind of scared of authorities :cool:
 
why are you notifying it? no one is allowed to come into my house to check my Electrical system lol, if you used to be a spark as you mentioned and know what you are doing then just get on with it. Okay back to the job, one thing I would say is whether the supply to the cabin at 4mm2 may be a little small and maybe a 6mm2 would be better, a freezer and light in the first shed is literally no load so there is some capacity for the log cabin, I would not go smaller than the original shed supply but that's me, by the way a lot of guys on here are newly out of college so my comments may shock them but lets be honest here, if it is your house then do what you want, just disconnect everything before you move hehe.
Cheers :) , I like that :cool:
 
I would like to do the job myself and get it certified by a registered electrician.

1. I do not wish to spend ÂŁ2000 on something I can do myself.
2. If possible, I would like to do the job base on a registered electrician's recommendation and his supervision (paid), which may also allow me to get my experience assessed for registration with a professional body like NAPIT.
I would not like to sign off any body's work, but give me that ÂŁ2000 grand and might think out it
 
I would not like to sign off any body's work, but give me that ÂŁ2000 grand and might think out it
Sorry mate, I would't want to pay 2 K for sign off, I meant the complete installation + Materials etc. For certification test I already have a quote ÂŁ180. :). Just a bit of supervision here is all I need because I have been away from this business for 25 years now
 
Thanks, reason for not involving an electrician in the physical job is as follows:
1. I do not wish to spend ÂŁ2000 on something I can do myself.
2. If possible, I would like to do the job base on a registered electrician's recommendation and his supervision (paid), which may also allow me to get my experience assessed for registration with a professional body like NAPIT.

I have the qualifications (full NVQ from Denmark, Industrial, Commercial and Residential) + UK 18th Edition, Part P and testing.

Yet here you are asking for advice on your proposed design.
 
Sorry mate, I would't want to pay 2 K for sign off, I meant the complete installation + Materials etc. For certification test I already have a quote ÂŁ180. :). Just a bit of supervision here is all I need because I have been away from this business for 25 years now
Why aren't you asking the person you have the ÂŁ180 quote from?
 
I'm sure there are quite a few who are registered with the TCP scheme that would look at signing off 3rd party work, otherwise they wouldn't have signed up to do so.

Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many those are prepared to sign off 3rd party work in which they've had no involvement during the design or installation stages.

My comment wasn't based on empirical evidence, rather an opinion based on general concensus of views read here and elsewhere. If you have any evidence based information on this subject I'd certainly be interested in reading it.
 

Reply to Feeding LogCabin from Shed CU in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
724
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top