Hi,

Please have a look at the sample PIR form - www.napitonline.com/downloads/Periodic Report Sample 01.09.pdf. I would like to know what the following means:

On page 4 of 4

  1. What “Figure 8 check” means. Do we really have to do it?
  2. Under Insulation resistance, what is IR between Live/Live, should we not have columns like Live/Neutral, Live/Earth & Neutral/Earth?
  3. Where we cannot remove all lamps (due to inaccessibility) while doing an IR test, we can connect L&N together read IR between L&N/E, and how do we record this?

Many thanks
 
Hi,

Please have a look at the sample PIR form - www.napitonline.com/downloads/Periodic Report Sample 01.09.pdf. I would like to know what the following means:

On page 4 of 4
  1. What “Figure 8 check” means. Do we really have to do it?Ring circuit check...also R1+R2 for a ring circuit....generally necessary,unless you are doing a limited scope PIR.
  2. Under Insulation resistance, what is IR between Live/Live, should we not have columns like Live/Neutral, Live/Earth & Neutral/Earth?....Phase-phase.
  3. Where we cannot remove all lamps (due to inaccessibility) while doing an IR test, we can connect L&N together read IR between L&N/E, and how do we record this?...record the same result in the L-E and N-E box.
Many thanks
.........................Link doesnt work,but that is my take on your queries.
 
Last edited by a moderator:
What “Figure 8 check” means. Do we really have to do it?
This means that you have successfully carried out the R1&R2 and R1&RN test with the cross connection "figure 8" method included.
Under Insulation resistance, what is IR between Live/Live, should we not have columns like Live/Neutral, Live/Earth & Neutral/Earth?
Live/Live means between Line and Neutral or between Lines (L1 to L2 for example), your interpretation of Live/Neutral and Live/Earth are incorrect because we now use the term Line for the Line conductor (not Live)
Where we cannot remove all lamps (due to inaccessibility) while doing an IR test, we can connect L&N together read IR between L&N/E, and how do we record this?
You would put it down as a limitation, and Live/Live column would likely be filled in as "Lim" in this scenario.
 
The link doesnt work for me

1.Figure 8 check is ring continuity test after end to end, at CU link L1 and N2 & L2 and N1 and test every socket outlet between L & N, then at CU link L1 and CPC2 & L2 and CPC1 and test every socket outlet between L & CPC. Readings should be within 0.05ohms
2.IR between Live/Live is between live conductors where both L & N are classed as live conductors
3. I just record this as live conductors to earth, on ECA forms its recorded as L-E IR
Regards gram
 
It means you are neither qualified nor are you competant to be carrying out PIRs or going by some of the questions being asked ANY electrical work
I understand the need to learn but doing this while charging money and with noone to make sure you are doing work correctly and within the regs ect is IMO WRONG
  1. What “Figure 8 check” means. Do we really
 
It means you are neither qualified nor are you competant to be carrying out PIRs or going by some of the questions being asked ANY electrical work
I understand the need to learn but doing this while charging money and with noone to make sure you are doing work correctly and within the regs ect is IMO WRONG
  1. What “Figure 8 check” means. Do we really

One would assume that's Napit's job?

or it should be.
 
This means that you have successfully carried out the R1&R2 and R1&RN test with the cross connection "figure 8" method included.

Widdler,

You know better than that, for ring circuit loops it is r[SUB]1[/SUB], r[SUB]2[/SUB] & r[SUB]n[/SUB] come on please! ;)

R[SUB]1[/SUB] & R[SUB]2[/SUB] are not actually "MEASURED" in a ring circuit now are they unless you have a spur off it.

There is no "official" definition of RN is there now, r[SUB]n[/SUB] more like, but that is not even on the brb model forms, or in the definitions.

BTW, not picking you up on the subscript thing, just read a post a few days ago on another website on how to do it!

:love:
 
Widdler,

You know better than that, for ring circuit loops it is r[SUB]1[/SUB], r[SUB]2[/SUB] & r[SUB]n[/SUB] come on please! ;)

R[SUB]1[/SUB] & R[SUB]2[/SUB] are not actually "MEASURED" in a ring circuit now are they unless you have a spur off it.

There is no "official" definition of RN is there now, r[SUB]n[/SUB] more like, but that is not even on the brb model forms, or in the definitions.

BTW, not picking you up on the subscript thing, just read a post a few days ago on another website on how to do it!

:love:

err.. no.

I was right.

:p
 
Widdler,
I have just gone through the definitions section of the brb, there is NO R[SUB]N[/SUB] defined, nor is there an R[SUB]n[/SUB].
Allowing for the fact that I have tried to use the subscripts, though it does not always work, and I'm not querying or criticising on the lack or otherwise of the subscript in your post, I understand the terms you use, but they are not defined in BS7671, or its associated guidance as I can remember.

In GN3 the term r[SUB]n[/SUB] is defined.

There is a big difference between r1+r2 & R1+R2.

Perhaps I did not explain myself when it comes to the way I used the term measured.

For a radial circuit, as installed, you can directly measure the R1+R2 values at the electrically extreme point of the circuit.

For a ring circuit, you can not directly measure the R1+R2 value as installed, you have to to some trickery with the wiring to get you this value do you not, which will always give the highest value at a spur.

You can only ever get r1, r2 & rn on a ring circuit by the way they are defined in GN3.

They don't appear any of them in the definitions section of BS7671, nor do they appear on the associated model forms.

Excluding Amd1 for the moment.

Does that clarify my post and standpoint?
 
Paul
I have just read the thread and the difference of opinion with Widdler

With reference to this comment by yourself
R[SUB]1[/SUB] & R[SUB]2[/SUB] are not actually "MEASURED" in a ring circuit now are they unless you have a spur off it.

An approximate value will be obtained with the end to end results calculated
A direct reading will be obtained at all sockets,ring and spurs when cross connecting


Or perhaps the opinions are more to do with direct readings,eg connections not altered ?
but, they are also altered for radials when a link is fitted
best I stay silent
[ElectriciansForums.net] Few questions on the PIR form
 
Last edited:

Reply to Few questions on the PIR form in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top