Can someone please explain why we have to cross conductors from legs of a ring to perform figure of 8 test (r1+r2 or rn+r1) and why we can't just link those conductors from the same leg as it would also make a loop... Would I be right in thinking that you would get a more even reading across both conductors when connected in figure of 8. Rather than the way I said as it would measure a much shorter distance. And would give inaccurate readings?
 
not only that, but by cross connecting, all your outlets should give the same value for R1+R2, unless there;s a spur off the rfc.
 
As tel said, easy way to locate spurs and loose connections.
If you don't connect them to opposites they will go up as you go along the ring then back down.
Like your loop readings will.
 

Reply to figure of 8 test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

Megger 15 series in my opinion are the best. Had a few 17 series that have put out err 23 codes. This is s an internal clock component issue...
Replies
2
Views
330
Darren dazz
D
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
687

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top