Your adding a new final circuit, so your inspector will be asking the question does it meet the requirements of BS7671.

How have you proved that it meets the requirements for volt drop etc.

Assessment to some degree of the sub circuits will be required unless you have sufficient information to allow otherwise.

Regards Chris
 
I think I am just going to have to make a detailed note on each certificate that I have visually inspected the sub-main circuits the best I can given the constraints of shut downs and access etc.

With reference to regulation 610.1 "Every installation shall, during erection and on completion before being put into service, be inspected and tested to verify, so far as is reasonably practical, that the requirements of the regulations have been met." Could I argue/explain that I have inspected and tested the circuits as far as is reasonably practical by using professional opinion that the sub-main circuits are suitable to use by the final circuit?

The discussion above drifted a little into the origin of supply being the major hurdle, most of this can normally be assertained as said by enquiry. It is mostly the shut down of sub-main circuits which we struggle with.
 
The bottom line to this is really your call and experience.

If you had a 70mm sub main from a bus bar chamber/ main switch panel going to a TP+N+E DB and the SWA feeding it looked good and on that board there were only 5 final circuits and the highest phase load was 13 amps, and you were asked to fit a new ring final on to it, there is a very good chance that it is not gonig to affect the existing installation so you do the tests on your EIC for your ring final and the Ze if you wish by enquiry.

On the other hand the 70mm is an old SWA, been in use for years, the TP+N+E Db is crammed solid with all sorts on it, with this lone spare way on it, you just manage becasue it is so crowded to clamp a phase, it is jumping all over the place with loads from 50-100 plus amps and they ask you to fit a new circuit, you might want to do a lot more testing and a lot more investigation.

The end of the day it is you that signs things off.
 

Reply to Final Circuit to Origin? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
682
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top