Thats a strange one.....on a conventional it would show the zone number in fault. Not sure what the new twinflex pro should show on zone earth fault.
im going to take lenth of cable tomorrow and hook it up , and if it sorts it il tell builder cable needs replaced and ceiling needs smashed , he not be happy
Remove all devices on the zone and check the cable first.....you don`t wont to smash the ceiling only to find a simple detector fault...as he really will be be happy then
Not sure if you can bypass earth fault monitoring on these but you shouldn't be doing that anyway. Defeats the object of it then.
If you are on site today and stuck, you could try giving Fike tech support a ring. They are extremely helpful and patient but I think Tazz may have nailed it to be honest with the cable fault.
all sorted , earth fault was on zone 2 but panel shows zone00 NA = twisted cable in the slack in ceiling.
s/c was twisted cable, had to cut holes and lucky it pulled between rooms . short distance = no faults
#lesson to be learned sloowdownniceandgentle
Reply to fire alarm fault and breathe......... in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
I challenged a council on having the same system installed in an HMO. One consideration is if the flats/escape route were made to The Building...
What was the make and model by the way?! What type of fire alarm too, most addressable systems you can simply add a relay output module to the...