Fire alarm fault zone advice | on ElectriciansForums

Discuss Fire alarm fault zone advice in the Commercial Electrical Advice area at ElectriciansForums.net

Joined
May 14, 2013
Messages
300
Reaction score
235
Location
Somewhere
Hi guys, I haven't done much in the past with fire alarms but am starting to get more work leads with them so it is something I want to get into. Does anybody have a fire alarm zone fault checklist they wouldn't mind sharing please and what are the most common FA panel keys? By the looks of things there are dozens of different types out there. Any advice or recommendations greatly appreciated.
 
Some panels may tell you the device that is at 'fault' and this just saves alot of head ache.

Others may tell you simply zone fault, sounder fault, general fault etc and will require reading the manufacturers data to determine what the actual fault could be. ( I recommend saving them as a pdf to your phone/tablet) possible psu fault, charger fault, battery fault.

I find tech helpline from apollo and Eaton very helpful.
 
What type are you starting with?
Conventional, bi-wire, addressable?
Different makes and types have their own quirky little faults.
How experienced are you in fire alarms?

Charlie, I am pretty much a beginner with FA's, only previous experience was running in the cables for the FA guy who then connected up the board and devices and did all the testing. We'll most likely be starting with conventional fire alarms in pubs and small commercial premises.
 
Are you doing any fire alarm testing?
If so, I recommend that you get your head round a fully functioning system, carry out test voltages whilst it is running and then observe voltages in an evacuation.
Once you get your head round the basic theory they are very simple, lot easier to fault find on than lighting installations.
Download some install manuals, lots of useful info in them
 
The first thing you should consider is CPD in fire alarm design, installation, maintenance and commissioning.

Until doing these courses I would stay well clear.
 
The first thing you should consider is CPD in fire alarm design, installation, maintenance and commissioning.

Until doing these courses I would stay well clear.

Would you say any is needed
To change a detector?
To change a battery?
To change a break glass?
 
Conventional panels are a lot harder to fualt find especially if something is intermittent I find myself fitting nerly always addressable systems even in small property’s the protec 6100 is also open protocol and compatible with the 6000plus range and you use less cable and a more professional system
 
Would you say any is needed
To change a detector?
To change a battery?
To change a break glass?

To be sure the detector you have installed is the correct one. To be sure the battery is correct for the installation and provides the correct level of back up. To ensure break glasses are in the correct position - YES.
 
Why would someone call out an electrician to replace the glass/plastic?

No I agree completely.
But it does happen.

I would and do change them as either non are onsite or staff do not know how to change them.

I have no fire alarm training and just asking other opinions.
 

Reply to Fire alarm fault zone advice in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

ESP - https://www.espuk.com/# is the company you are referring to part of Scolmore
Replies
2
Views
298
  • Question
If the wiring can't be corrected , the best solution is to get a cheap 1 loop addressable fire alarm panel and create a loop and install isolators...
    • Like
2
Replies
38
Views
5K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
487
Some of the points should have been picked up by previous people doing the testing. Sounds like this is a thorough report. Not everything is...
Replies
11
Views
2K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks