T
tazz
Bs5839 changed in 2002, Mains feed to fire alarm panels must be wired in enhanced fire proof cable, this can be enhanced fp200 or piro. Mains feed can be off db now or essential supply db. A lockable double pole switched fused spur must used to feed the control panel located near by. Usual 17th regs apply to cabling such as protection by rbo/rcd etc where the control panel must have battery backup and warning incase of mains failure. A lot better than the old days of comming straight off the incoming with a BS88 fuse