Time is money no matter what and it's horses for courses (especially in France!) as to what you charge.The guy who charges £30/hour doesn't (as pointed out earlier) have (as an overalll company) 405,000 employees worldwide and all that entails,nor does he or she have shareholders.They also haven't invested time and money into R&D for new products - it all adds up.
If I was self-employed I could bill myself out at £30/hour and be happy with that - our cost price is much more than that.
Totally agree, this is why i sub out the installation to know sparks. As stated this has always been a good partneship for me.
To be fair, Tazz, design is as much an issue inside the "fire" industry as out - taking the broader whole. Many electricians I know are probably better, certainly at install, than many so-called fire alarm engineers.
Fire design (and commissioning) is a distinct expertise in itself, IMO.
110% there Bill - I don't touch install of cables if I can get away with it because (i) it'll look like a dogs hind leg,(ii) it'll take me all day running in 5 metres and (iii) it'll still look like a dogs hind leg!!
Where some contractoors are still falling down on is the look of surprise because they have to use metal P clips instead of plastic nailed clips,metal ties instead of plastic as sole means of support and "what do you mean a double pole isolator with special switch?"!
Ah......interestingly, System Sensor make the claim of being the largest global manufacturer of fire detection products - but I'd say Siemens were pretty well up there too.
7,000,000 Sinteso heads sold last year worldwide (but then,statistics are wonderful things!).
Rediculous IMO....£360 for 3 hours worth of plugging in a flamin laptop!
Oh, how I hate this forum sometimes. I've just typed a reply to your post, and watched it disappear as I mis-keyed, deleting the lot, rather than the one letter I wanted to.
However, it's probably well that I try to respond with brevity.
I did start off by pointing out what a commissioning visit should cover, and why it costs the way it does. I think, in the end I will put it in a new thread presently, as it was quite long.
For the moment though, £120 an hour for commissioning on a closed licence system is not expensive at all when you consider all the factors that go into making up that rate, such as development of the protocol, the knowledge that had to be trained into the guy wielding the laptop, not just of the program he's using, but also of the wider fire standards, and laws. Getting him there.
The key thing is that the DESIGNER, should have made the end customer (your customer I guess) aware that these costs were part of the cost of having that system, because of the nature of the protocol it runs on.
The key difference is that open licence manufacturers tend to design the protocol in line with the standards, to do what their devices should. BUT. They then pass on the responsibility for the rest of it to you. This method passes on all responsibility for correctness of design, suitability for application, correct operation, and more to you.
Most closed licence manufacturers retain that responsibility - and in effect, would let you off the hook if it came to court.
I wanted to say that whilst in many ways fire commissioning isn't at all unlike signing off on an EIR or PIR, there are differences.
Electrical systems have designed in safety, such as fuses, breakers, RCDs, isolators, and overload protections, which ensure in most cases that the worst that can happen is a loss of service.
Fire has no such fail-safes. The fire system ends up being the very last line before death is the most likely outcome, rather than just a minimal risk factor.
That's why closed protocol manufacturers need to ensure they cover the cost of knowing that any system out there using their kit is 100% right in the field. Without that certainty, and the costs it bears for development, commissioning and so forth, it is THEM in court when someone dies, and not you.
Open licence manufacturers take the view that you had the ability and competence to take on that responsibility yourself, and the end result is that YOU end up in court if it all goes barbeque.
In that sense, using a licenced system can be an insurance as much as anything - similar to employing a design engineer to sign off on the design of a large electrical system.
Mostly, commissioning fees are set at a rate they are, because there are massive development costs to recover, as well as intensive training for the guys who do the commissioning (as I say not just in the system, but in knowing how to make it comply fully with the law, standards, and other legislation), and the cost of making sure that it all stays relevant, and available.
I'll try to make a better job of my points a little later.
Yes, biggest install fail I come across even now - plastic clips!!!!!!!!!!!!
That, and plastic cable ties when the cable isn't supported by the metal tray it is tie wrapped to!!!!
It's always fun trying to explain to customers that their installation doesn't meet the required standard, because of a bit of plastic.
That's a few. Statistically, we've purchased around 6500 heads this year so far, and I can honestly say I don't think one of them was a Sinteso.......
Not sure what the System Sensor output was - very probably not 7 million though!
It's a fair claim in my book! And an indication of how successful a closed licence system can be!
..and just to show that SP203 is a paper making excercise - seen a site this time last year (which was a new install in a school) that had been installed by the companys preferred installer and commissioned by the company themselves which had been installed completely in plastic conduit and saddles throughout (up and along walls,across ceilings etc.).Lovely neat job right enough but goes to show that you can't be even sure with an approved company.
Outside of the UK in Europe every other public bulding has a Siemens system installed (Germany it is nearing 100%)....sorry,this has turned into a marketing thread!!
The issue is that in the UK closed protocol systems have been seen as being returning revenue schemes,which is of course a part of it but that shouldn't be the only thing and a sole reason to flleece customers (past and present).We are trying to get away from this mentality as we recognise the bad reputation it gives and prefer to show that our systems have unique features and are backward compatible.
And they wonder why some of us still say MICC should have stayed.
Sad thing is that most of them hide behind the fact that the cable is fire rated, completely oblivious to the fact that when the plastic "containment" fails pretty fast, that fire rated cable is going to become a pretty thorough trip hazard, or death noose.
And that's before you assume that the additional weight of the cable having to support itself may well disconnect it from the installation.
As for SP203...........
paper making exercise is probably the politest way of putting it......
So essentially then the gist so far is that calling ones self a 'specialist' in a given area, is a licence to print money and people will either pay it or risk death because no-one else is capable of carrying out the job other than the 'specialist'???
To be honest I would prefer a specialist take the responsibility and the fall if it went terribly wrong. They are charging for the risk as well as their time and at the end of the day it's the commercial customer footing the bill. Personal opinion
As I said,a specialist company isn't just a "closed protocol" company - it's a company that specializes and understands what fire alarms are about,and the risk involved in getting any part of it wrong.
It isn't a licence therefore to print money but generally the specialist company will have actually invested in training their employees properly,rather than just allowing the new start to pick it up from the old guy who remembers the days when you could wire the lot in T&E (actually,if it's an L1 addressable system with isolators on each device there's no reason why (aside from it being in the standard of course!) why you can't wire it in 0.7mm belden cable!).
Please read the thread fully as you're missing the point....I already stated that I use a company for supply and commision on a regular basis.
The problem I have is with the closed system specialist equipment manufacturers and their 'pay us or die' ethic who charge way over the top for adding devices to a system that has been disigned and installed by someone else so even if there was a problem that went to court they would stand from under with the "we didn't design or install your honour" stand.
So by paying their extortionate fee they havn't taken the resposibility off you at all.
Lenny - methinks you might be taking it a bit on the general side, comparing your lemon to an apple........
That's not the gist at all -and certainly not the one intended.
Anyone can call themselves a "specialist" in any field they choose. To actually be one is a different matter.
An analogy might be that a policeman does so many years as a "general" policeman, learning the common parts of that job, and has to do that BEFORE he can become say a drugs officer, or a traffic officer, firearms, whatever.
And so it is with fire as a specialism.
There are thousands of guys out there calling themselves fire alarm engineers. Most of them are nothing of the sort.
To get to a level of "commissioning" (or designing), typically, you need to have several years active experience of fire alarm engineering, and you need to demonstrate also that you are fully conversant with not just BS 5839 and EN54, but also related fire legislation - the RRO, HASAW, EAWR, BS9999, COSHH, and many more. Until 2007, we had to be familiar with potentially over 120 different pieces of legislation affecting fire safety. The legislation that replaced most of those isn't much better - as in the main it simply passes responsibility to the owner of the premises in question. In turn, that responsibility is passed to the "specialists" coming in claiming to know how to repudiate that risk.
There's a big difference between being a specialist in the area of fire detection or safety, as against say an AV specialist.
Also, what about IT support? Rates of £200 an hour for software engineers are common - and the protocol argument stands perfectly there too, the moment you choose to have a bespoke bulletin board, over an off the shelf one.
When it comes right down to it, almost anyone is capable of carrying out even specialist fire work - with the right knowledge and tools.
Your notion sort of falls on its head a little every time you moan about a DIY'er getting it wrong, and end up having to put right several incorrectly wired plate switches, or sort out an intermediate switch the DIY'er couldn't get his head around, as well as having borrowed neutrals in.
The point, in your case - the £360 - you were paying for the use of the licenced protocol as well as the guy's time - as I said, there's another layer in that charging over and above using open licence kit - but that said, call Apollo out to a system that isn't doing what you think it should - they'll charge a similar level for their engineers (who, incidentally mostly have that extra layer of knowledge and training too, mostly because Apollo would not want the bad press associated with their protocol, should the fire system fail).
It isn't about calling yourself "specialist" and hiking the cost up - theres far more to it than that.
Hope this doesn`t become sparks vs fire. Personally as stated we work together, yes we do advised the electricians and state standards. But in the end we all get there. Again my view only, is I would not hold an electrical contractor down to a closed system, unless we were supporting it. As Bill stated his experience is his electrical contractors do a first class job compared to some said Fire alarm installers. Buzard, you are well ofay to your systems, and can support them which is more to the point. Lenny if you are being held to paticular closed system may be idea to state like other electrical contractor that you wish a open system.
I've already been told that to do this would be unwise for future work that may may or may not come my way!!!
I apologise if any of this has come across the wrong way but essentially I'm being held to ransom by a particular company and there genuinely isn't anything I can do about it.
Lenny Surely they would make you aware of any non compliance issues with your existing system, as they are connecting into it they are responsible for the commissioning and installation of their own equipment and so shouldn't be connecting something into a system that is deemed unsuitable before installation, if they do then the responsibility rests with them for commissioning part of a system that was non compliant to start with. So if your open system is fully compliant already and their part of the system fails, in court it's down to them.
Lenny no need to appologise, this is forum not a court of law. on many of your contractors who is requesting the closed system? as I cannot understand why the job cant be seen through till the end. As buzard uses a closed system, his company would be there from design till end. Which is the same ussual proceedure for any open system
It isn't a pay us or die ethic, Lenny.
I grant that it is a case of pay for the commissioning or do without.
But that was, or should have been, a consideration for both the designer and the owner at the the time of design of the system, when that particular protocol was established.
If you use them that regularly, why not explore the option of becoming approved by them, and reducing cost that way? I don't know which company you're moaning about of course.
When they sign off on the commissioning of the devices added, they ARE taking responsibility for the design of the system - it is NOT retrospective in any way. And trust me, it will be them in court, should the system fail at any point after those changes, and should it result in criminal damage or loss of life. The owner's insurance company will make pretty damn sure of that.
The point is, that protocol was designed into the system for a reason, we presume. That's part of the cost overall of using that protocol in that system, and from a purely commercial point of view is why folks need to understand "cost of ownership" as a terminology, rather than "how much to get the fire officer off my back and stop the place getting closed down".
Thing is, who are you going to come after if your customer phones you to say he's just lost his business premises, all his business records, and thirty people got burned to death because the fire alarm didn't work? On an open or unlicenced protocol system, there's only one place to go - the person with responsibility for the system - you, if you were the last person working on that system. Then your insurer is going to start looking closely with the customer's insurer, at how you did the work, how you tested it, how you designed it, what care you took to ensure the system worked at the time, why it didn't work when it needed to and so on. They'll look at you, and your qualifications, expertise, competence, and when they decide that you were "only an electrician" (sad, but true), they'll throw the proverbial book at you.
That's the risk any company involved in fire alarm systems takes every day. While it seems extreme, it is all fact, and evidence exists everywhere to bear out what I say.
The key difference between an electrical installation, and a fire alarm system, generally, is that an electrical system whilst a potential risk to life, has so many levels of in built protection to ensure that risk is mitigated as far as possible. A fire detection system, by nature cannot have that. It relies 100% on knowledge - of design principally, to do what it needs to in the event of fire. It can't shut the fire down on its own, but by all accounts it absolutely must provide the earliest possible warning that fire has broken out.
No, that's not true.
Look - I didn't want this to descend into some sort of one "trade" is better than another - but I did want it understood that, certainly in the case of fire, a specialism really is a specialism, and not just a way of making money.
The truth is, while our commissioning rates are roughly twice what our general labour rates are, the margin on commissioning is no greater - we "make" exactly the same amount per hour on commissioning as we do on cable pulling. But for my commissioning guys, I have extra layers of cost that my cable pulling guys don't attract - training and education, extra kit and tools, market forces (I want the best guys, not just guys who know how to use a laptop), and so on.
Manufacturers are the same - they need to pay for protection of their protocol, development of it, development of the detection that works with it, development of the control panels that work with it, knowledge of the standards and requirements at all levels to ensure their kit will comply when installed, and will continue to do so as changes take place, as well as all the stuff I have to pay my commissioners for.
It all comes back to the original point - DESIGN.
There was (probably) a reason that licenced protocol system was used over and above anything available off the shelf - why was that? Particular C&E requirements, size of system, other reason?
That's why, today, you're paying £120 an hour for use of the protocol, and continued design protection - as I say, the design is not retrospective - it applies at the point of commission, and as such, that bod with his plug in lappy, is your man when the barbeque starts, whether he likes it or not.
Hey, don't get defensive mate. None of us are beating you with a stick, only trying to explain how that situation comes about and why.
And no need at all to apologise - your views on this are every bit as valid as anyone else's.
Its about understanding both sides - and helping out if we can.
I get your point totally, and I've had the same frustrations over and over -
specifically "why" a closed or licenced protocol system was used when an open one would have done the job just fine.
But no, there isn't much you can do about it, if you're stuck with the protocol.
What you can do, though, is explore options for getting more hands on with that protocol, and in the mean while, explain to the customer the reasons why charges are so high, and that ANY maintenance company is going to charge that cost on.
Who's the company involved?
I think Lennys experience though does show how NOT to sell the benefits of an "in house" system if they client feels cheated somewhat afterwards - this is something that the companies involved need to get away from.
Interestingly,Apollo had mentioned licencing their protocol so that you couldn't just walk into ADI and buy a C-TEC with Apollo and install it without having a current dongle (or similar) but I haven't heard anything of this in a while but maybe ALL manufacturers need to be on board with this idea to keep the cowboys/chancers away from the configuring side of the fire system.All systems are maintainable by any one competent and devices can be changed like for like without having to use a laptop (in most cases - not sure about Protec as have only had the "pleasure" the once!).
I know this thread is over a year old but I have recently Joined Apollo and found this thread particularlly informative.
Although I am currently working on another research project, it is my intention to quantify and publish the state of the current open/closed protocol situation.
It would be appreciated if the individuals that have contributed to this thread email me , so I can issue a short survey based upon your experience's.
The results of the study will be sent to the participants. Thankyou and hope this is a step in the right direction to educating the end users.
[email protected]
An even bigger problem with closed operating protocol is one that i have had the misfortune to encounter where the Project BMS was a different manufacturer to the Fire Alarm company!! Neither were willing to give the other company there operating protocol so that the 2 systems could talk to each other!! We are talking here about a massive Project site, with literary many thousands of control points on each system. Yes it was a very big mistake in the first place having two separate systems/manufacturers, and if it hadn't have been caught in time, an astronomically expensive fix would have been required!!!
I wonder if anyone here, can visualise what would have been needed to overcome this situation?? A clue would be the inclusion of ASCI codes..
In the end, the fire alarm manufacturer was dropped from the contract, and a variation order made to the BMS system for the inclusion of there fire alarm modules. Which was a shame, as the BMS system was Crap with a capital ''C''
Fire Alarm Open/Close protocol
Security Alarms, Door Entry and CCTV (Public)
tazz,
Engineer54,