Been meaning to post something up about this for a week or two but never had a chance, its a bit long winded but stick with it!
A company i do the maintenance for asked me to bring a spark in to look at a fire alarm panel they were having bother with, the company that maintains the alarms for the group had been called in a fortnight before for some issue with the panel.
Two engineers had already been to the job, the first guy replaced a fuse and all was well, the second guy (1 week later) replaced the panel and added a load of extra stuff as he reckoned something in the stores DB was pulling too much current and knacked the fire alarm panel. This guy put a seperate PSU and relay in but when he powered it up something was clicking in the DB so he left it and i got the phone call to bring a spark in.
Me and my spark went in and it turns out the guy who added all the extras in has left the alarm company, the new guy they sent up didnt seem to know much tbh and seemed to be relying on my spark to put his alarm panel back to how it should be for him.
We found a knackered relay in the DB which is energised by 24v from the fire alarm panel and in turn energises a 240v coil contactor that switches the air con on. Obviously this is so the air con is switched off in the event of a fire. Left at at that and went and bought a new relay the next day.
My spark has got a new job working away so i took a guy from the forum back with me so we could plug the relay in and try it out. Plugged the relay in and nothing, we manually operated the relay with the toggle on the top and sure enough the contactor pulled in and the A/C switched on. Checked the AUX output from the alarm panel and there was nothing.
We found a 24v output from inside the alarm panel that cut out when we triggered a call point and connected this up to the aux cable to the relay in the DB, This pulled the relay/contactor in and everything was working fine.
I got a phone call a couple of days later to say the alarm panel was beeping so i called in to have a look, it was in fault mode and was showing an earth fault and a sounder fault. Being confident the electrical side was ok i told them to get the Fire alarm company back out as it needs checking that all the terminations are in the right place as its been messed on with that much! the alarm guy came out again and says there is still something wrong with electrical side??
I called in today to get some pics and draw a wiring diagram up to post on here and see what the opinions are, while i was there i looked inside the fire alarm panel and the engineer has disconnected the 24v aux supply and it seems to be working fine as there was no air con in the store and it was mega hot i flipped the toggle on the relay to bring the air con on but obviously the fire alarm has no control over it at the minute which needs sorting.
Relay and contactors in an enclosure under the DB
Alarm Panel Connections
I though i had a picture of the extra bits that have been added but it doesnt look like i have
Also the alarm panel seems to be a Gent Xenex but there are no details on the unit...
Let me know if i havent explained anything correctly, i knew nothing at all about fire alarms before this job but i'm getting my head around the way operate a little now
Stu
A company i do the maintenance for asked me to bring a spark in to look at a fire alarm panel they were having bother with, the company that maintains the alarms for the group had been called in a fortnight before for some issue with the panel.
Two engineers had already been to the job, the first guy replaced a fuse and all was well, the second guy (1 week later) replaced the panel and added a load of extra stuff as he reckoned something in the stores DB was pulling too much current and knacked the fire alarm panel. This guy put a seperate PSU and relay in but when he powered it up something was clicking in the DB so he left it and i got the phone call to bring a spark in.
Me and my spark went in and it turns out the guy who added all the extras in has left the alarm company, the new guy they sent up didnt seem to know much tbh and seemed to be relying on my spark to put his alarm panel back to how it should be for him.
We found a knackered relay in the DB which is energised by 24v from the fire alarm panel and in turn energises a 240v coil contactor that switches the air con on. Obviously this is so the air con is switched off in the event of a fire. Left at at that and went and bought a new relay the next day.
My spark has got a new job working away so i took a guy from the forum back with me so we could plug the relay in and try it out. Plugged the relay in and nothing, we manually operated the relay with the toggle on the top and sure enough the contactor pulled in and the A/C switched on. Checked the AUX output from the alarm panel and there was nothing.
We found a 24v output from inside the alarm panel that cut out when we triggered a call point and connected this up to the aux cable to the relay in the DB, This pulled the relay/contactor in and everything was working fine.
I got a phone call a couple of days later to say the alarm panel was beeping so i called in to have a look, it was in fault mode and was showing an earth fault and a sounder fault. Being confident the electrical side was ok i told them to get the Fire alarm company back out as it needs checking that all the terminations are in the right place as its been messed on with that much! the alarm guy came out again and says there is still something wrong with electrical side??
I called in today to get some pics and draw a wiring diagram up to post on here and see what the opinions are, while i was there i looked inside the fire alarm panel and the engineer has disconnected the 24v aux supply and it seems to be working fine as there was no air con in the store and it was mega hot i flipped the toggle on the relay to bring the air con on but obviously the fire alarm has no control over it at the minute which needs sorting.
Relay and contactors in an enclosure under the DB
Alarm Panel Connections
I though i had a picture of the extra bits that have been added but it doesnt look like i have
Also the alarm panel seems to be a Gent Xenex but there are no details on the unit...
Let me know if i havent explained anything correctly, i knew nothing at all about fire alarms before this job but i'm getting my head around the way operate a little now
Stu