Detectors no further apart than 7M, any void greater than 800mm in height will require detection, remote indicators for concealed voids, interface units for any mechanical plant, MCP's at each external exit door and at each change of compartment.
If they are to be seperate units, you will need to asses the cause & effect of an alarm situation. Any electronically operated doors will also require interfacing, additional beacons in disabled W/C's, sound levels need to be assessed with additional visual indication if necessary.
The above is a brief outline of things to consider, your own risk assessment will highlight & pinpoint any other issues.
Maintenance of the system is as important as the installation
Design of a fire alarm system is a minefield and remember, its your arse on the line if it all goes pear shaped.
As Sotty said, input from those concerned will be paramount.
Hope this helps.