how often does a fp 200 need to be p clipped, is it every clip or can a p clip be used in between plastic clips also with wire suspension system could how often would I need to use a metal tie wrap

many thanks
 
how often does a fp 200 need to be p clipped, is it every clip or can a p clip be used in between plastic clips also with wire suspension system could how often would I need to use a metal tie wrap

many thanks

Installed lots of fp200 in hospitals and we always have to p clip every 250mm on solid walls (no plastic and on tray or basket metal zip ties every 400mm hope this helps :)
 
how often does a fp 200 need to be p clipped, is it every clip or can a p clip be used in between plastic clips also with wire suspension system could how often would I need to use a metal tie wrap

many thanks

Metal clips 250mm horizontal, 400mm vertical.

If in plastic conduit then saddles must be metal.

If in plastic mini trunking then cable must be clipped with metal clips inside the trunking.

Cable below 2m should be mechanically protected.

All BS5839

Cheers, Ron
 

Reply to fire alarm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
514
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

It's galvanised and provided you coat any cut edges with galv spray there should be no signs of undue corrosion any time soon. Galv trunking...
Replies
7
Views
538
nicebutdim
N
I challenged a council on having the same system installed in an HMO. One consideration is if the flats/escape route were made to The Building...
Replies
1
Views
427

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top