Hi,

I need to install a fire control panel in a communal hallway and this is my first time. Can anyone provide any guidance as to decibel level or the units I should install?

Many thanks,

Ken
 
Off top of my head i think minimum is 65dB for most areas, but if needed to be heard in flats etc usual attenuation levels for internal doors is 20dB so would need to be highter for required level to be heard on the other side. Google bs5839 you should find most answers maybe even purchase this.
 
From memory, i think for open corridors and areas, it's something like measuring 80/85db from X amount of metres. I'll have to check that with our spec though!!
 
Bs5839 all areas need minimium of 65db, if a siren is maked up as 103db output, then this is the measurement at 1 meter. Rule of thumb, every meter you can loose aprox 10db, through a fire door or doors you will loose aprox 15-20db. Best method is put sirens on alternative walls were possible. In a large hall 1 siren should cover 20m x 20m or 400m Sq
 

Reply to Fire alarms 93db or 103db? in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
793
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
979

Similar threads

I challenged a council on having the same system installed in an HMO. One consideration is if the flats/escape route were made to The Building...
Replies
1
Views
437
Have you checked the RJ 45 type lead that connects the pcb to the power supply in behind is properly connected? What voltages do you get at the...
Replies
1
Views
204

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top