Please correct me if I'm wrong lads:-
Why would you need RCD protection in a none residential building unless its a spec for schools etc?
If it is a 230V fire alarm system, why would you have it on an RCD (apart from safety) which could be switched off from a nuisance trip not related to the fire alarm? (back up batterys I can understand).
These are questions for my own understanding more than anything else.
Cables buried in walls at depths of <50mm which do not incorporate earthed armouring or sheath would require additional 30mA RCD protection regardless of the building the installation was in. However, i cannot imagine a school having a 230V fire alarm system not wired in MICC (pyro) and i would imagine it unlikely that they would have a 230V system at all considering the level of renovation that is going on in most UK schools in my experience.