You need to consider what the light is intended to do.
Some installations such as Cinemas, Theaters or even Night clubs require emergency exit signs to be lit whenever the installation is being used.
Other installations only require the light to be lit in the event of a power failure.
Other's again only require the light to be lit in the event of a fire.
In most cases, feeding the light off of the locall lighting circuit rather than a dedicated circuit is preferable, as it will light up on battery if that local circuit fails, rather than wait for the whole installation to fail.
 
BS5266 does not specifically tell you where you can and cannot feed a self-contained emergency light from.

You can feed the light from where ever you like.

All that matters is the emergency lighting operates upon failure of the normal lighting.

In my opinion the sensible solution is to feed the self-contained emergency lighting from the same MCB/fuse (via key switch) which feeds the normal lighting in that area.
 
Last edited by a moderator:
Ther's no real need for a key switch, as testing can be achieved through switching off the relevant MCB.

It would make duration testing of the emergency lighting very awkward.

Say if it was schedule to be done late one day and its dark outside, you don’t want to lose your normal lighting, especially if the school is occupied.
 
Last edited by a moderator:
Ther's no real need for a key switch, as testing can be achieved through switching off the relevant MCB.

Just found this:-

BS5266-1:2011 8.3.3

Each emergency lighting system should have a suitable means for simulating failure of the normal supply for test purposes (i.e. without interruption of the normal supply)
 
Last edited by a moderator:
This looks to be an old document as it does not mention The Regulatory Reform (Fire Safety) Order 2005 which supersedes a lot of the legislation mentioned

Yeah just had a look, it’s really really old.

BS5266-1:2005 was revised in December 2011, Superseding BS5266-10:2008 as well.
 
Last edited by a moderator:
Just found this:-

BS5266-1:2011 8.3.3

Each emergency lighting system should have a suitable means for simulating failure of the normal supply for test purposes (i.e. without interruption of the normal supply)

The problem I have with such a method, is that would not show whether the Lux levels are sufficient. Only by interupting the normal supply could that be assessed.
 
The problem I have with such a method, is that would not show whether the Lux levels are sufficient. Only by interupting the normal supply could that be assessed.

I normally if say i have a local grid switch with one key a one switch my load from the key would also feed the switch so i am not interupting the normal supply to areas not on test
 
Just got this last year from the NICEIC stating it was new and just released by the BSI, been well had over, good of the nic knocking out their old crap along with the old PIR's

well miffed

Sorry my mistake, I’m getting my years mixed up.

BS5266-1:2005 was superseded in December 2011
 

Reply to fire exit sign in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I've looked at the fire assessment from the last HMO I did for the same landlord and fire assessor, the risk assessment is pretty worthless, it's...
Replies
7
Views
1K
Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
671

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top