• Please use style selector to select BLUE AND WHITE. If you are not already on it. This notice will go once you're on the correct style.

Fire panel & detectors system

Hopefully someone who works with these regularly can hit me with some sort of tip here. Hotel owner I know decided to change all his detectors now it’s coming up general fault on the panel. I’m guessing he hasn’t noted in & out on cables before replacing but he’s sure he did. He also says it’s an old eol resistor he has in, probably at least 25 years old! Is it just a case of taking each head off & checking voltage is same going into diode & out of it? Any quicker ways to locate the fault? I’ve installed these a handful of times over the years but never fault finding on them.
 
It sounds like an conventional/analogue system as opposed to addressable.
Given owner has changed heads himself, I'd first check he has used compatible units. Did he change the bases too?
Zones normally have their own fault indicators, are these lit too?
Otherwise "General Fault" suggests a sounder circuit fault.
Fault finding on conventional usually boils down to moving the resistor/EOL devices around until it's happy, including trying them at the panel itself, and then working out from that where the problem is, then checking cables can connections. Sorry to say they can be a right pain.
 
eol device must be fitted at the last detector/sounder on the zone. if youhave more than one eolthen the panel will see this as a fault. a head not fitted correctly will also show fault.
 
eol device must be fitted at the last detector/sounder on the zone. if youhave more than one eolthen the panel will see this as a fault. a head not fitted correctly will also show fault.
To clarify i was only advocating moving it for diagnosis purposes, not as any kind of permanent solution!
 
To clarify i was only advocating moving it for diagnosis purposes, not as any kind of permanent solution!
didn't mean to oppose your post. understand what you mean, proving panel can see eol along the line.just saying.
 
Hotel owner meddling with a potentially life critical system....shakes head and slaps face ?, meanwhile I assume hotel is without a fire system now, lets hope they are not taking guests in.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Back
Top