Extract from BS5839 pt1 2002
All systems need to be wired in fire resistant cable, junction boxes, clips and terminations. Some domestic (BS 5839-6) systems need to comply with BS 5839- 1. These are Grades A and B systems. These systems also require fire resistant wiring.
25.2 Recommendations for mains power supplies
25.2 c) 'To facilitate local isolation during maintenance, suitable means should be provided for the double pole isolation of the low voltage supply circuit that serves the power supply and the control equipment(see 29.2e)'
29.2 Electrical safety recommendations
29.2 e) ' Means should be provided for double pole isolation of the mains supply to all parts of the system; the isolation facilities should be suitably sited , in the vicinity of the equipment served, for use by maintenance technicians without the need for access to remote parts of the building. It should be possible to lock the facilities in both the normal and isolate positions to prevent unauthorised use. See Clause 25.'
29.2 f) 'Every isolator, switch and protective device that can isolate the supply to the fire alarm system, other than the main isolator for the building, should be labelled either;
FIRE ALARM; Protective device serving only the fire alarm with no switch
FIRE ALARM, DO NOT SWITCH OFF; in the case of a switch (whether incorporating a protective device or not) that serves only the fire alarm circuit.
29.2 g) Every isolator, switch and protective device that is capable of disconnecting the mains supply to the fire alarm system should be situated in a position inaccessible to unauthorised persons or be protected against unauthorized operation by persons without a special tool
Note 4 A special tool, may for example, be a key actuator (sometimes called "secret key") for a mains switch device.
So to summarise, Wired in fire resistant cable, requires double pole spur with key most use the fish tail keys and it needs to have marked on the face plate "FIRE ALARM, DO NOT SWITCH OFF"