From Hager’s manufacturers instructions
Read the cable entry part
Extract below
For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above.
Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.
View attachment 60338
Also
cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than:
· 1.0 mm for the horizontal top surface and
· 2.5 mm for all other surfaces of the enclosure that are accessible after installation.
So in conclusion, flame retardant or whatever you want to call it , grommets are not required but are not precluded, an inspector cannot fail or say it is unsatisfactory if you have not used them and quoting regulation 421.1.201 is pointless as that regulation does not specify such things.
A metal consumer unit is not a fire barrier, I mean for god sake there’s combustible mcb’s and devices installed In it.