Generally flame retardent is used to describe an item/product which has been treated or chemically altered so that it resists catching fire or is self extinguishing.

Generally a fire retardent is a substance which is used to slow down a fire, or fight a fire. The foam in a foam fire extinguisher is a fire retardent.

Looks like the CEF ones are better value then :) !
 
Please specify the reg that you believe needs complying with.
421.1.201 that’s the one
[automerge]1598139945[/automerge]
Please specify the reg that you believe needs complying with.
I’ll be honest here, reason why I know this is because I got picked up on it by inspector A year ago when I used open grommets on consumer up tight to ceiling without proper fire sealing it and making sure it’s an enclosed chamber to prevent the escape of fire. He recommended the flame retardant grommets
 
The intent of Regulation 421.1.201 is considered to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames. Like so much else, it depends on your interpretation of the word "reasonably".
 
The intent of Regulation 421.1.201 is considered to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames. Like so much else, it depends on your interpretation of the word "reasonably".
I agree, just speaking from experience the inspector didn’t like open or blind grommets, I did though until then lol
 
421.1.201 that’s the one
[automerge]1598139945[/automerge]

I’ll be honest here, reason why I know this is because I got picked up on it by inspector A year ago when I used open grommets on consumer up tight to ceiling without proper fire sealing it and making sure it’s an enclosed chamber to prevent the escape of fire. He recommended the flame retardant grommets
As usual, The regs manage to make things more complicated by not being clear about their requirements and leaving it to people to find a way that most people thing complies.

I'd have thought open grommets wouldn't meet the IP rating for the top surface of a consumer unit in any case?

But all reg 421.1.201 really says is that consumer units should be manufactured from non-combustible material. It says nothing about any subsequent holes that you create in the thing during installation (it probably should imo). When using rear entry holes then there is not even an available flame retardant option that I'm aware of? Partly because they are not standard.

I've seen several of the Youtubers talk of filling the rear gaps with flame retardant sealant, but that doesn't seem to be a regulation, just an idea of 'good practise' that has grown up while people try to interpret what a reg means.

And since for CUs the only suitable example of non-combustible given is ferrous metal then if the reg applied to connections they'd also have to say that all grommets should be metal to be consistent, which isn't exactly going to work.

A lot of the meter tail glands now recommended are plastic anyway, and likely not flame retardant (Wiska do make one similar to their FR grommets having said that)

Personally I use the FR grommets because they are easy to force cables through (including post installation) and seal fairly well afterwards and although more expensive than blind grommets the cost is small compared to a consumer unit on a job.
 
Inspector of what? The building inspector?
[automerge]1598141883[/automerge]


That regulation says non-combustible, flame retardent is not non-combustible, these are different things.
Inspector from Council I done work for, it also states that cable entry points should be adequately sealed it’s a grey area but one which I unfortunately got made a mug out of. He had a couple of pages printed out in front of me and the main boss I can try and find them now and send the link IET I think it was from
[automerge]1598142923[/automerge]
Inspector from Council I done work for, it also states that cable entry points should be adequately sealed it’s a grey area but one which I unfortunately got made a mug out of. He had a couple of pages printed out in front of me and the main boss I can try and find them now and send the link IET I think it was from
[ElectriciansForums.net] Fire Retardant Grommets
 
Last edited:
Rather than grommets what about thsee ...

 
Rather than grommets what about thsee ...


I consider that to be false advertising.

Polyamide (nylon as it is often know as) is not fire proof.
It can be made self extinguishing with the right addatives

Just take a blow torch to one and see just how “fireproof” it really is.
 
From Hager’s manufacturers instructions
Read the cable entry part
Extract below

For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above.
Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.
[ElectriciansForums.net] Fire Retardant Grommets
Also

cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than:
· 1.0 mm for the horizontal top surface and
· 2.5 mm for all other surfaces of the enclosure that are accessible after installation.

So in conclusion, flame retardant or whatever you want to call it , grommets are not required but are not precluded, an inspector cannot fail or say it is unsatisfactory if you have not used them and quoting regulation 421.1.201 is pointless as that regulation does not specify such things.
A metal consumer unit is not a fire barrier, I mean for god sake there’s combustible mcb’s and devices installed In it.
 
Last edited:
Ok , what about these ?

 
From Hager’s manufacturers instructions
Read the cable entry part
Extract below

For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above.
Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.
View attachment 60338
Also

cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than:
· 1.0 mm for the horizontal top surface and
· 2.5 mm for all other surfaces of the enclosure that are accessible after installation.

So in conclusion, flame retardant or whatever you want to call it , grommets are not required but are not precluded, an inspector cannot fail or say it is unsatisfactory if you have not used them and quoting regulation 421.1.201 is pointless as that regulation does not specify such things.
A metal consumer unit is not a fire barrier, I mean for god sake there’s combustible mcb’s and devices installed In it.

Agree whole heartedly.

However BS7671is not always our only requirement to follow.

Often with big companies/councils there are adopted working practices which are the result of personal preference, which is fine if agreed to in advance.

Whats annoying is where you are not made aware of these foibles, don't do them and they try to make out its "best practice" or "in the regs".
 

Reply to Fire Retardant Grommets in the Electrical Tools and Products area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top