Hi, just wondering if anyone would be kind enough to take a look over my cable calc as I haven't done one really since I finished college as it's all been house bashing.
The customer wants a supply feed up to the top of his garden (cable run will be 70m) The cable is to be run along the top of a fence so I have used reference method C. And I have also used the ambient temperature of 30 degrees (but im not too sure if this is right)
The cable is to feed a jacuzzi from homebase (guessing no more than 4kw, it cost ÂŁ300) a summerhouse which consists of a socket for general use (probably a tv) and a light fitting. It is also to feed some garden lighting.
A pond with a water pump may also be added at a later date.
I've estimated the power consumption to be around 9kw.
9kw@230v = 39A
The cable does not run through any thermal insulation nor is it grouped with any other cables. Is there any other derating factors I should be looking at?
10mm - 1 two-core cable, single phase ac - 67A (table 4D4A - pg280)
Voltage Drop
4.4 mv/a/m = 4.4x39Ax70m/1000 = 12v
Max permissible VD for 230v is 6.9v (3%)???
So I think I need to either use a larger cable or restrict the usage? Just 10mm seems an awful lot for a few lights and a jacuzzi. I think the next step would be to find the exact rating of the jacuzzi.
I know this is really basic for alot of you but it's been a long day, and what feels like a really long time since i've done this!
Any advice would be greatly appreciated!
The customer wants a supply feed up to the top of his garden (cable run will be 70m) The cable is to be run along the top of a fence so I have used reference method C. And I have also used the ambient temperature of 30 degrees (but im not too sure if this is right)
The cable is to feed a jacuzzi from homebase (guessing no more than 4kw, it cost ÂŁ300) a summerhouse which consists of a socket for general use (probably a tv) and a light fitting. It is also to feed some garden lighting.
A pond with a water pump may also be added at a later date.
I've estimated the power consumption to be around 9kw.
9kw@230v = 39A
The cable does not run through any thermal insulation nor is it grouped with any other cables. Is there any other derating factors I should be looking at?
10mm - 1 two-core cable, single phase ac - 67A (table 4D4A - pg280)
Voltage Drop
4.4 mv/a/m = 4.4x39Ax70m/1000 = 12v
Max permissible VD for 230v is 6.9v (3%)???
So I think I need to either use a larger cable or restrict the usage? Just 10mm seems an awful lot for a few lights and a jacuzzi. I think the next step would be to find the exact rating of the jacuzzi.
I know this is really basic for alot of you but it's been a long day, and what feels like a really long time since i've done this!
Any advice would be greatly appreciated!