first day done of my AM2 exam. Just wanted to let people know what I done and if I will loose any marks.

So first of all risk assessment and safe isolation. I completed the risk assessment no problem at all and the safe isolation I completed fine as well asked for permission to isolate, prove, test, prove, lock off and warning notices, key in pocket etc.

Install section:-

Lighting cicuit took 1.5mm twin and earth L and Neutral and cpc to my first switch, fed the common with my L and Neutral in the back switch. I then took a 3 core 1.5 to the second swith which was grey as my neutral which went into the back of the wago, brown as my S/L with brown tape and the other brown as my other S/L. To the intermideate I then took the 3 core and looped the Grey in the back as a Neutral again, then took my brown and black to the top or the intermediate. Again, sleeved correctly. Another 3 core out to my last switch done the same again brown/ black S/L and neutral into another wago. Then, 1.5 up to the light as my neutral in the wago and the brown into th common. All cpc linked in wago is back of switch as well. MCB 6 Amp Type B

Ring Main

2.5mm and 1.5mm cpc from db to first socket, though to the spur, and to the last socket, last socket then back to the db. Then took 2.5 and 1.5 to the outdoor socket on the load side of the Switched spur. Ring on a 32 amp RCBO type B.

Bonding
10mm for water and seperate for gas.
Gas to first part of the pipe before the T joint.
Water connection just after the stopcock/ first section of pipe. Back to the db seperate and labeled.

Fb 200

Supply from DB to non switched spur. From
Non switched spur up to co2 alarm. A seperate length of FB 200 On cable tray using P clips and bolted to the tray. tighting of glands etc also on a Mcb 6 amp type B.

3 phase and neutral isolator. 4 core 2.5mm from db to isolator, again banjo and glanded at both ends. Used 1.5mm cpc as bonding cable inside db for the banjo. Then 2.5mm 3 phase colours and 1.5mm cpc to commando socket. Then looped neutral in back of isolator using a wago. 3 phase and earth connections.

3 phase dol starter

3 phase, neutral and cpc to dol starter.
Sy 3 core and earth to motor box. Glanded off and cable tied to cable tray. Marked 1 as L1 , 2 as the Black phase and 3 as the Grey phase.

S heating plan ill do tommorow along with thermal overload to work out of the motor and the data points. I still have 3 hours left.

Does all sound good? Or any hints or tips on things ive missed out?

Inspection and testing tommorow and fault finding

Cheers!
 
first day done of my AM2 exam. Just wanted to let people know what I done and if I will loose any marks.

So first of all risk assessment and safe isolation. I completed the risk assessment no problem at all and the safe isolation I completed fine as well asked for permission to isolate, prove, test, prove, lock off and warning notices, key in pocket etc.

Install section:-

Lighting cicuit took 1.5mm twin and earth L and Neutral and cpc to my first switch, fed the common with my L and Neutral in the back switch. I then took a 3 core 1.5 to the second swith which was grey as my neutral which went into the back of the wago, brown as my S/L with brown tape and the other brown as my other S/L. To the intermideate I then took the 3 core and looped the Grey in the back as a Neutral again, then took my brown and black to the top or the intermediate. Again, sleeved correctly. Another 3 core out to my last switch done the same again brown/ black S/L and neutral into another wago. Then, 1.5 up to the light as my neutral in the wago and the brown into th common. All cpc linked in wago is back of switch as well. MCB 6 Amp Type B

Ring Main

2.5mm and 1.5mm cpc from db to first socket, though to the spur, and to the last socket, last socket then back to the db. Then took 2.5 and 1.5 to the outdoor socket on the load side of the Switched spur. Ring on a 32 amp RCBO type B.

Bonding
10mm for water and seperate for gas.
Gas to first part of the pipe before the T joint.
Water connection just after the stopcock/ first section of pipe. Back to the db seperate and labeled.

Fb 200

Supply from DB to non switched spur. From
Non switched spur up to co2 alarm. A seperate length of FB 200 On cable tray using P clips and bolted to the tray. tighting of glands etc also on a Mcb 6 amp type B.

3 phase and neutral isolator. 4 core 2.5mm from db to isolator, again banjo and glanded at both ends. Used 1.5mm cpc as bonding cable inside db for the banjo. Then 2.5mm 3 phase colours and 1.5mm cpc to commando socket. Then looped neutral in back of isolator using a wago. 3 phase and earth connections.

3 phase dol starter

3 phase, neutral and cpc to dol starter.
Sy 3 core and earth to motor box. Glanded off and cable tied to cable tray. Marked 1 as L1 , 2 as the Black phase and 3 as the Grey phase.

S heating plan ill do tommorow along with thermal overload to work out of the motor and the data points. I still have 3 hours left.

Does all sound good? Or any hints or tips on things ive missed out?

Inspection and testing tommorow and fault finding

Cheers!
Don't call it a Ring main, (Ring Final Circuit)
 
Erm I might be reading it wrong but you’ve took a live and neutral feed to 1st switch but then taken a 3 core and earth to 2nd switch and for an intermediate switch for 2 and 3 way control.
If so then why have you made the grey from the 3 core a neutral?
If it’s 2 way then black as common marked with brown over sleeving and the grey wants oversleeving brown also as it’s a strapper.
The only neutral you should have in the switch is the mains fed one from the DB then out to your light.

If I’ve miss read your txt then ignore me.
 
Erm I might be reading it wrong but you’ve took a live and neutrals feed to 1st switch but then taken a 3 core and earth to 2nd switch and an intermediate switch for 2 and 3 way control.
If so then why have you made the grey from the 3 core a neutral?
If it’s 2 way then black as common marked with brown over sleeving and the grey wants oversleeving brown also as it’s a strapper.
The only neutral you should have in the switch is the mains fed one from the DB then out to your light.

If I’ve miss read your txt then ignore me.
I may be wrong, but I think the OP has taken a L and N to the first switch on a 2 way switching circuit and has carried the N conductor through to the second switch and at the 2nd he will have a 3core, 2 strappers and a N at that switch where he will then run a 2 core and earth from the light, this cable will be a N and SL, again if I have read the post wrong then ignore this post.
 
Do you not take a mains from the DB to the first light switch then your s/live and neutral to the light wired from the first switch (which is a 2 way)containing your permanent live and neutral?
Any 2 way and intermediate switches then it’s just 3 core from your first switch to your intermediate then a 3 core from your intermediate switch to last 2 way switch.
Why carry a neutral all the way through?
 
On the AM2 they require a neutral at each switching point on the lighting circuit.

So T&E from MCB to 1st switch. 3C&E to intermediate and 3rd switch, then T&E to luminaire.

Technically you can use an colour core for strappers, neutral etc as long as their identified/sleeved.
 
Do you not take a mains from the DB to the first light switch then your s/live and neutral to the light wired from the first switch (which is a 2 way)containing your permanent live and neutral?
Any 2 way and intermediate switches then it’s just 3 core from your first switch to your intermediate then a 3 core from your intermediate switch to last 2 way switch.
Why carry a neutral all the way through?
Because he has to take SL and N from the last switch in the line
 
On the AM2 they require a neutral at each switching point on the lighting circuit.

So T&E from MCB to 1st switch. 3C&E to intermediate and 3rd switch, then T&E to luminaire.

Technically you can use an colour core for strappers, neutral etc as long as their identified/sleeved.
So there’s a neutral at the intermediate switch? Which is pointless.
Am I reading that right?
Different from when I did it.
It was about 17 years ago mind
 
Last edited:
Erm I might be reading it wrong but you’ve took a live and neutral feed to 1st switch but then taken a 3 core and earth to 2nd switch and for an intermediate switch for 2 and 3 way control.
If so then why have you made the grey from the 3 core a neutral?
If it’s 2 way then black as common marked with brown over sleeving and the grey wants oversleeving brown also as it’s a strapper.
The only neutral you should have in the switch is the mains fed one from the DB then out to your light.

If I’ve miss read your txt then ignore me.

Oh well I wired it as this drawing is drawn. You have to loop a neutral in the back of the switches. So I took a L and N to the first switch to feed the common and Neutral in the back of the switch.

Then a 3 core taking two S/L to the intermediate from the first switch. Looped Neutral in the back again. Then a length of 3 core to the other 2 way switch which has a 2 S/L’s and a neutral. Again looped in the back. Picked uo the neutral in the back and up to the light on a seperate 1.5 which then brown to the common up to the light ?

Is this wrong? Or right?

I just followed this drawing.
 
Heres the drawing

[ElectriciansForums.net] First Day of AM2 exam finished! Just need alittle bit of help.
 
On the AM2 they require a neutral at each switching point on the lighting circuit.

So T&E from MCB to 1st switch. 3C&E to intermediate and 3rd switch, then T&E to luminaire.

Technically you can use an colour core for strappers, neutral etc as long as their identified/sleeved.

So what ive done is correct then in my exam? Im panicing like hell now!?!?
 
Oh well I wired it as this drawing is drawn. You have to loop a neutral in the back of the switches. So I took a L and N to the first switch to feed the common and Neutral in the back of the switch.

Then a 3 core taking two S/L to the intermediate from the first switch. Looped Neutral in the back again. Then a length of 3 core to the other 2 way switch which has a 2 S/L’s and a neutral. Again looped in the back. Picked uo the neutral in the back and up to the light on a seperate 1.5 which then brown to the common up to the light ?

Is this wrong? Or right?

I just followed this drawing.
Do it as per drawing Ryan it’s what you have to do and it shows you can read drawings also.
 
So there’s a neutral at the intermediate switch? Which is pointless.
Am I reading that right?
Different from when I did it.
It was about 17 years ago mind
There will be a N at all 3 switches in a wago I should imagine or some other connector.
 

Reply to First Day of AM2 exam finished! Just need alittle bit of help. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top