Hi I have just finished the new 2394 course and thought I would perform a EICR on a friends house, little did I know what a state the installation is in. Any help or recommendations would be great as I have a lot to learn.The main consumer unit is around 20 years old with a mixture of 3871, 60898 rcd /rcbo and 4293 breakers. The first surprise was the missing main protective bonding conductors to the Gas and Water services would this rate a C2?Both bathrooms had mains voltage downlights in zone 1 with no IP rating and no RCD protection would this still rate a C2 as potentially dangerous?There was no equilpotential bonding anywhere in the property eg bathrooms/kitchen. C3?The downstairs ring main has no rcd protection for cables buried less than 50mm. C3The installation in general was very poor with connections made at lighting plates with chocblocks and Sellotape, 5-6 mm of bare conductors showing and Cpc's of kitchen ring main wired into the rear metal backbox instead of the socket terminals. (surprisingly Zs value ok)The list was exhausting what a way to learn!As a seasoned bunch of electricians would you recommend the consumer unit be updated to 17th?Replace light fittings with suitable elv IP rated downlights?Run main earth bonding conductors to gas and water services?I think my neighbour is going to be shocked when I list the observations, as they believe the installation is safe, it looks as if they have been done over by cowboys every time they have had some work done.Again thank you in advance for your combined wisdom.