Hi all
Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block.
Carried out a ZE test got 14 ohms and got same reading when did ZS on the board (yes did disconnect earth for ZE) .. the main earth is wired into the service block .. I’m guessing the orange cable is going to a main fuse in the plant room and is armoured ..
Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block.
Carried out a ZE test got 14 ohms and got same reading when did ZS on the board (yes did disconnect earth for ZE) .. the main earth is wired into the service block .. I’m guessing the orange cable is going to a main fuse in the plant room and is armoured ..
- TL;DR
- Should the ze be done from the earth block rather than the main from the service head ??
I.e connect earth from MFT to block them probe onto terminals inside the DB ??