I had a bit of a head scratcher today, I think I've got to the bottom of it but thought I would run it past you guys.

0.15MΩ between N and CPC on a ring circuit.

I started breaking down the circuit and when I disconnected one of the sockets the fault cleared. I now got 15MΩ. Nothing obvious to see, but it cleared so I was happy.
I then started putting the sockets back on. One of the sockets was a spur and it was feeding another spur. Before I put this socket back on I IR tested both cables, to eliminate the possibility of the fault being on the cable leading to the (2nd) spur. It tested fine, however, the cable feeding the first spur came up with an IR reading of 0.0MΩ. I then did a continuity test and got 0.1Ω (N-E)

I then retested the whole ring, and still got 15MΩ, even with the spur testing at 0.1Ω (N-E).

My plug in tester had indicated that all was ok when I was initially determining which sockets were on the circuit (i.e 3 lights showing on the tester).

I then did a R1 + R2 which showed me the CPC was broken.

I then calmed down and realised that the CPC must be completely broken, but something was causing continuity between the N-E.

I'm now thinking a screw through the cable, but how likely is it that a screw would completely severe the CPC and then make contact with the neutral, but actually only be in contact with one part of the now broken CPC?

Another thought is that the screw has been removed, somehow leaving the neutral still touching one part of the broken CPC?

Another thought is that the CPC is actually connected to the neutral in the JB under the floorboards?

Just thought I'd check if I'm missing anything obvious before I start chopping in to the wall or taking up floorboards?
 
Faulty sockets perhaps?

Or earthed faceplate screws pressing into neutral wire?

Another (hidden) socket or joint box?
A spur from a spur? Has there been a lot of bad alterations?

 

Reply to Todays fault finding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

Similar threads

Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
855
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top