Dayo it has just the start stop
hi seadog60,
I used to wire / install / commission control panels a while back and the reason lots of control panels / motor circuits have 110v or 24vdc coils is to reduce the risk from a safety aspect.
The reason they did this was because the start / stop pushbuttons were normally mounted on the metal doors of the enclosure and by wiring the coils in 24vdc you would only have a potential of 24vdc at the door or if the control circuit was wired in 110v you would only have the potential of 55v at the door (usually a centre tapped transformer, same principal as your 110v yellow site leads)
If you need a hand with wiring diagrams etc let me know and i am more than happy to help.
Steve.
Hi Tony,Sorry to correct you but nearly all 110V control systems are end tapped to earth. The reason being that an earth fault could hold a coil in making the e-stop inoperative.